Understanding General Requirements of the NEC, Part 9
Article 110 provides general requirements for all installations. Sec. 110.14 provides the general requirements for electrical connections. The first requirement is that any connectors (e.g., pressure terminal connectors) must be identified for the material of the conductor. You can’t mix and match the metals. The second requirement is that you install them properly. There’s some additional text, then the remaining requirements are organized as follows:
(A) Terminals. Gist: Make sure connections to these are mechanically secure without damaging the conductors.
(B) Splices. Gist: Any splicing devices shall be identified for the use.
(C) Temperature Limitations. Gist: The limiting value is the lowest rating of any connected termination, conductor, or device. A chain is only as strong as its weakest link.
(D) Terminal Connection Torque. Gist: Tighter isn’t necessarily better, use the correct torque value.
Common violations of Sec. 110.14 include crushing a connector instead of crimping it, using three conductors in a connector rated for only two, using copper lugs on aluminum conductors, using a higher temperature column in the ampacity table than the lowest rated connector or using a connector that is rated lower than the temperature column used to determine ampacity, and overtightening of connections. Perhaps the least recognized of 110.14 violations is the overtightening of connections.
When you tighten to the correct torque value, you obtain maximum clamping power; going past that point dramatically decreases clamping power. If you have a Bellville washer, you tighten it until it’s just hitting flat. If you have a split ring lock washer, you tighten the connection just enough to close the ring (like the Belleville washer, it will be just hitting flat). A split ring washer compressed this way will exert maximum pressure against the threads, locking them into place. If you crush the spring out of the washer, it is then essentially a flat washer and no longer contributes to making the connection mechanically secure.
Mark LamendolaMark Lamendola
Related
Understanding General Requirements of the NEC, Part 1
A finger presses a green key on a keyboard that says 'NEC National Electrical Code'