What’s Wrong Here? Hint: This Cover Needs to Be Corrected
Hint: This cover needs to be corrected.
For 125V and 250V, 15A and 20A receptacles installed in wet locations, Sec. 406.9(B)(1) requires the enclosure to be weatherproof whether or not an attachment plug cap is inserted into the receptacle. The type of flip-open cover installed here is only weatherproof when it is closed. In fact, this cover is marked “wet location when cover closed.” This particular cover is supposed to be installed so the covers flip up to open rather than flipping left or right to open. Replacing this cover with a weatherproof while in use cover, such as a “bubble cover,” would be one way to provide a weatherproof enclosure. This area is not subjected to routine high-pressure spray washing, so the exception in Sec. 406.9(B)(1) allowing “weatherproof when closed” covers is not applicable here. Lastly, the UF cable should probably have some protection from physical damage, such as a rigid conduit sleeve, since those blue soda can racks could easily smash the cable.
Russ LeBlanc
Russ LeBlanc