• NFPA 70E: Annex Marks the Spot — Part 3
    Informative Annex D summarizes the methods available for calculating arc flash boundary and incident energy.
    June 21, 2024
    3 min read
    This annex summarizes four methods in D.2 through D.5. They are:
    D.2. Ralph Lee Calculation Method. This method is often preferred for systems that are outside of the IEEE 1584-2018 range of model. It’s named after Dr. Ralph H. Lee, an influential figure in arc flash study. His landmark paper, “The Other Electrical Hazard: Electric Arc Blast Burns,” was published in 1982. In D.2., you’ll find basic equations, sample calculations, and calculations of incident energy exposure greater than 600V for an arc flash hazard analysis. There are two tables and a single-line diagram along with this.
    D.3. Doughty Neal Paper. If you know the maximum bolted fault current and want to determine the energy at a given distance (e.g., where the exposed worker will be working), this method will provide the correct answer. This paper was written by A. Bingham, R. Doughty, and T. Neal in the mid-1990s. They used empirical test data at various distances from a fault. In D.3, you’ll see how to estimate the incident energy for an arc in open air versus one in a cubic box.
    D.4. IEEE 1584-2018 Calculation Method. If your parameters fit the model range of parameters used in this method, this is a good method to use. It is not recommended to attempt using the equations for conditions outside the stated test ranges. In D.4, you get some good background information on using this method. That includes Table D.4.4., which provides the range of input parameters.
    D.5. Direct Current Incident Energy Calculations. You would use this when you want to calculate dc arc flash incident energy. As D.5.1 says, “This method is based on the concept that the maximum power possible in a dc arc will occur when the arcing voltage is one-half the system voltage.”
    Annex D doesn’t teach you how to perform these calculations. It gives you an overview, which in itself is useful even if you never aspire to being a “qualified person” when it comes to actually performing these calculations. Understanding some of what is involved in these calculations is good because you have a deeper understanding of what those numbers mean and how even small changes may affect you.