Code Q&A: Connections and Splices
Courtesy of www.MikeHolt.com. Based on the 2023 NEC.
Question: All _____ that are spliced or terminated within the box shall be connected together. Connections and splices shall be made in accordance with Sec. 110.14(B) and Sec. 250.8 except that insulation shall not be required.
a) neutral conductors
b) equipment grounding conductors
c) phase conductors
d) switch-legs
See answer below.
Answer: b) equipment grounding conductors
Per Sec. 250.148(A): "All equipment grounding conductors that are spliced or terminated within the box shall be connected together. Connections and splices shall be made in accordance with 110.14(B) and 250.8 except that insulation shall not be required."
Mike Holt
Mike Holt