Code Q&A: Grounding Requirements for a Building
Test your NEC knowledge.
May 27, 2021
Q. What is the Code rule for connecting a grounding electrode system to a building supplied by a feeder?
See answer below.
A. As per Sec. 250.32, a building supplied by a feeder must have a grounding electrode system and a grounding electrode conductor installed in accordance with Part III of Art. 250.
Exception: A grounding electrode is not required for a building if it is supplied by a single branch circuit or multiwire branch circuit.
CAUTION: To prevent dangerous objectionable neutral current from flowing on metal parts [Sec. 250.6(A)], the supply circuit neutral conductor is not permitted to be connected to the remote building disconnect enclosure [Sec. 250.142(B)] (Figure above).
Mike Holt
Mike Holt