Q. What identification is required by the NEC for neutral conductors?

 See answer below.

A. Section 200.6 of the 2020 NEC outlines the identification requirements for grounded conductors.

200.6(A) 6 AWG or Smaller

Neutral conductors 6 AWG and smaller must be identified by any of the following means (Figure):

(1) Insulated conductors with a continuous white outer finish.

(2) Insulated conductors with a continuous gray outer finish.

(3) Insulated conductors with three continuous white or gray stripes along its entire length on other than green insulation.

(4) Insulated conductors with their outer covering finished to show a white or gray color but have colored tracer threads in the braid identifying the source of manufacture.

Author comment: The use of white tape, paint, or other methods of identification is not permitted for neutral conductors 6 AWG and smaller.

200.6(B) 4 AWG or Larger

Neutral conductors 4 AWG or larger must be identified by any of the following means:

(1) A continuous white outer finish along their entire length.

(2) A continuous gray outer finish along their entire length.

(3) Three continuous white or gray stripes along their length.

(4) White or gray tape or markings at the terminations.

200.6(E) Neutral Conductors of Multiconductor Cables

Insulated neutral conductor(s) sized 6 AWG and smaller in multiconductor cables must be identified by a continuous white or gray outer finish, or by three continuous white or gray stripes. Conductors in multiconductor cables sized 4 AWG or larger can have the neutral conductor identified in accordance with Sec. 200.6(B).

Exception No. 1: Conductors within multiconductor cables are permitted to be re-identified at their terminations at the time of installation by a distinctive white or gray marking.

These materials are provided to us by Mike Holt Enterprises in Leesburg, Fla. To view Code training materials offered by this company, visit www.mikeholt.com/code

About the Author

Mike Holt

Mike Holt is the owner of Mike Holt Enterprises (www.MikeHolt.com), one of the largest electrical publishers in the United States. He earned a master's degree in the Business Administration Program (MBA) from the University of Miami. He earned his reputation as a National Electrical Code (NEC) expert by working his way up through the electrical trade. Formally a construction editor for two different trade publications, Mike started his career as an apprentice electrician and eventually became a master electrician, an electrical inspector, a contractor, and an educator. Mike has taught more than 1,000 classes on 30 different electrical-related subjects — ranging from alarm installations to exam preparation and voltage drop calculations. He continues to produce seminars, videos, books, and online training for the trade as well as contribute monthly Code content to EC&M magazine.

Voice your opinion!

To join the conversation, and become an exclusive member of EC&M, create an account today!

Sponsored Recommendations

Latest from Q&A

ID 376312510 © Евгений Полишко | Dreamstime.com
dreamstime_xl_376312510
ID 367959703 © Suphachai Panyacharoen | Dreamstime.com
dreamstime_xl_367959703
ID 8209371 © Indiloo | Dreamstime.com
dreamstime_xl_8209371

Sponsored