Two or more grounding electrodes that are bonded together are considered a single grounding electrode system.

Q. What does the Code require in regard to installing a grounding electrode using ground rods?

A. Grounding electrode system installation requirements are outlined in Sec. 250.53.

(A) Rod electrodes

(1) Below permanent moisture level. If practicable, pipe electrodes must be embedded below the permanent moisture level and be free from nonconductive coatings such as paint or enamel.

(2) Supplemental electrode. A rod electrode must be supplemented by an additional electrode that’s bonded to:

(1) Another rod electrode

(2) The grounding electrode conductor

(3) The service neutral conductor

(4) A nonflexible metal service raceway

(5) The service disconnect

Exception: A single rod electrode having a contact resistance to the earth of 25 ohms or less isn’t required to have a supplemental electrode.

Author’s comment: Generally, a single ground rod won’t have a contact resistance to earth of 25 ohms or less. In many cases, a ground rod with a supplemental electrode (two rod electrodes) won’t have a contact resistance to earth of 25 ohms or less. However, the maximum number of rod electrodes required by the NEC is two regardless of the contact resistance.

(3) Spacing. The supplemental electrode for a rod electrode must be installed not less than 6 ft from the rod electrode.

(B) Electrode spacing. Electrodes for premises systems must be located no closer than 6 ft from lightning protection system grounding electrodes. Two or more grounding electrodes that are bonded together are considered a single grounding electrode system (Figure).

(C) Grounding electrode bonding jumper. Grounding electrode bonding jumpers must be copper when within 18 in. of the earth [250.64(A)], be securely fastened to the surface, and be protected from physical damage [250.64(B)]. The bonding jumper to each electrode must be sized in accordance with 250.66.

Author’s comment: The grounding electrode bonding jumpers must terminate by any of the following means in accordance with Sec. 250.8(A):

  • Listed pressure connectors
  • Terminal bars
  • Pressure connectors listed as grounding and bonding equipment
  • Exothermic welding
  • Machine screw-type fasteners that engage not less than two threads or are secured with a nut
  • Thread-forming machine screws that engage not less than two threads in the enclosure
  • Connections that are part of a listed assembly
  • Other listed means

When the termination is encased in concrete or buried, the termination fittings must be listed for this purpose [250.70].

These materials are provided to us by Mike Holt Enterprises in Leesburg, Fla. To view Code training materials offered by this company, visit www.mikeholt.com/code

About the Author

Mike Holt

Mike Holt is the owner of Mike Holt Enterprises (www.MikeHolt.com), one of the largest electrical publishers in the United States. He earned a master's degree in the Business Administration Program (MBA) from the University of Miami. He earned his reputation as a National Electrical Code (NEC) expert by working his way up through the electrical trade. Formally a construction editor for two different trade publications, Mike started his career as an apprentice electrician and eventually became a master electrician, an electrical inspector, a contractor, and an educator. Mike has taught more than 1,000 classes on 30 different electrical-related subjects — ranging from alarm installations to exam preparation and voltage drop calculations. He continues to produce seminars, videos, books, and online training for the trade as well as contribute monthly Code content to EC&M magazine.

Voice your opinion!

To join the conversation, and become an exclusive member of EC&M, create an account today!

Sponsored Recommendations

Latest from Q&A

ID 367959703 © Suphachai Panyacharoen | Dreamstime.com
dreamstime_xl_367959703
ID 8209371 © Indiloo | Dreamstime.com
dreamstime_xl_8209371
ID 57245818 © Mrchan | Dreamstime.com
dreamstime_xl_57245818

Sponsored