Q. What is the Code rule that applies if two or more branch circuits supply devices or equipment on the same yoke?
A.  If two or more branch circuits supply devices or equipment on the same yoke, a means to disconnect simultaneously all ungrounded conductors that supply those devices or equipment is required at the point where the branch circuit originates [210.7].
A yoke, also called a strap, is the metal mounting structure for a receptacle, switch, switch with pilot light, switch-receptacle, and so forth. Individual single-pole circuit breakers with handle ties identified for the purpose, or a circuit breaker with a common internal trip, can be used for this application [240.15(B)(1)].