Practically Speaking: Examining a Potentially Expensive Requirement
Why the requirements of Sec. 210.63 have the potential to be a big (and expensive) requirement to comply with.
The idea to require a 125V, 15A or 20A receptacle outlet within 25 ft of panelboards, switchboards, switchgear, and motor control centers in other than dwelling units may not seem like a big deal at first. However, when we breakdown the requirements in Sec. 210.63, we may come to realize that this could sometimes be a really big deal — and a potentially very expensive requirement. These receptacles could be needed for power monitoring equipment, other portable equipment, or tools. An installation as basic as the one shown in the Photo (with the receptacle outlet located beneath the panelboard enclosure) could be problematic.
The requirements in Sec. 210.63(B)(2) do not allow the required receptacle outlet to be connected to the load side of the panelboard’s main breaker. This means the installation in the photo would not comply with the present requirement because the receptacle outlet is fed from this panelboard. In fact, none of the branch circuits in this panelboard could be used to provide power to the receptacle outlet required by Sec. 210.63, since all of those circuits are on the load side of the main breaker for this panelboard.
What if this is the only panelboard in the building? Well, in that case, the cost to comply with Sec. 210.63 goes way up. Adding a second panelboard with another 125V, 15A or 20A receptacle outlet fed from that second panelboard would be one way to comply. Of course, each receptacle outlet would need to be within 25 ft of the other panelboard to provide a Code-compliant installation.
What if the building only has 277V/480V power? I have worked in a few pump houses that only had panelboards feeding 480V motors and 277V lighting, but no 120V circuits. In buildings such as this, a transformer would be needed to provide the 120V circuits needed for the required receptacle outlets. But keep in mind the required receptacle outlets cannot be on the load side of the panelboard’s disconnecting means, so at least two panelboards would be required — each with a receptacle outlet installed to serve the other panelboards.
What if the building is fed by a feeder with one switchgear as the main disconnect for the whole building? Well, guess what? The required receptacle cannot be on the load side of the disconnect for that switchgear. Watch for revisions in the Code to provide some relief for this requirement in 2026.
Russ LeBlanc
Russ LeBlanc