Two TIAs Proposed for 2023 NEC Regarding Sec. 210.8(A)
The National Fire Protection Association (NFPA) recently released two proposed Tentative Interim Amendments (TIA) to the 2023 Edition of the National Electrical Code (NEC). The TIAs were submitted by Greg Woyczynski, Association of Home Appliance Manufacturers (AHAM), and have a comment closing date of September 6, 2023.
The proposed revisions are as follows:
TIA Log No.: 1748
Reference: 210.8(A) Exception No. 5 (new)
1. Add a new Exception No. 5 to section 210.8(A) to read as follows:
210.8(A) Dwelling Units.
Exception No. 5: GFCI protection shall not be required for a receptacle serving a refrigerator or HVAC appliance if all of the following conditions are met:
(1) The appliance is located within a dedicated space.
(2) The appliance is on an individual branch circuit.
(3) In normal use, the appliance is not easily moved or is fastened in place.
This exception shall expire January 1, 2028.
A detailed substantiation for TIA 1748 can be read here.
TIA Log No.: 1749
Reference: 210.8(A) Exception No. 6 (new), and 210.8(D) Exception (new)
1. Add a new Exception No. 6 to section 210.8(A) to read as follows:
Exception No. 6: GFCI protection shall not be required for a receptacle serving an electric range, wall-mounted oven, counter-mounted cooking unit, or microwave oven if both of the following conditions are met:
(2) In normal use, the appliance is not easily moved or is fastened in place.
2. Add a new Exception to section 210.8(D) to read as follows:
210.8(D) Specific Appliances.
Exception: GFCI protection shall not be required for an outlet supplying an electric range, wall-mounted oven, counter-mounted cooking unit, or microwave oven if both of the following conditions are met:
A detailed substantiation for TIA 1749 can be read here.