NEC Requirements for Fuel Cell Systems
Article 692 of the 2020 National Electrical Code (NEC) provides the requirements for installing fuel cell systems. At less than two pages, this Article is short compared to the Articles covering wind and solar. If we consider wind and solar “primary” energy sources, fuel cells would be “secondary” because the fuel (typically hydrogen) is chemically generated rather than collected from nature. Fuel cells are typically delivered as units.
Some key points:
- The fuel cell nameplate provides its rated current [Sec. 692.8(A)].
- The ampacity of the feeder circuit conductors to the premises wiring can't be less than the nameplate rated current or the rating of the fuel cell OCPD(s), whichever is greater [Sec. 692.8(B)].
- If OCPDs sufficient to protect the circuit conductors that supply the load are provided, the fuel cell needs no additional OCPDs [Sec. 692.9(A)].
- The system must have a means of disconnecting all current-carrying conductors from all other conductors in a building [Sec. 692.13].
- Because a fuel cell is a power source, it is grounded. Be sure the grounding complies with Sec. 692.41.
- Use a separate equipment grounding conductor (EGC) [Sec. 692.44] sized per Sec. 250.122 [Sec. 692.45].