Vitalij Sova/iStock/Getty Images Plus
Welding
NEC Rules for Grounding Electric Welders
Feb. 19, 2019
Article 630 requirements for arc welders and resistance welders
Article 630 of the NEC distinguishes between arc welders and resistance welders, with separate requirements for each (in Part II and Part III, respectively).
  • A resistance welder flows current through the two materials to weld them; the heat for the weld is a function of the resistances of the materials being welded.
  • An arc welder creates a weld when electric current arcs between an electrode and the material being welded on; you’re melting the electrode (welding rod) to create the weld.
    In both situations, you need a return path for current.
With the resistance welder, you squeeze two parts between weld tips. That arrangement provides the return path.
With an arc welder, you create the return path by connecting the “ground” lead to “ground.” And therein lies a source of great confusion. It’s common practice to connect the “ground” lead to building steel, but that connection makes the current return through hundreds of connections of varying impedance. Instead, provide a return conductor from the welder to the same disconnecting device its power comes from.