Fig. 1. The area of all conductors at any cross section does not exceed 40% of the cross-sectional area of that space.
Stumped by the Code? NEC Requirements Related to Panelboards
April 14, 2023
Answering your NEC questions
Courtesy of www.MikeHolt.com
All questions and answers are based on the 2023 NEC.
Q. What are the NEC requirements related to cabinets for panelboards related to repairing gaps in noncombustible surfaces?
A. The requirements related to cabinets for panelboards associated with repairing gaps in noncombustible surfaces are found in Sec. 312.4. Recessed cabinets for panelboards and cutout boxes in noncombustible surfaces (plaster, drywall, or plasterboard) must not have a gap of more than 1⁄8 in. around any edge of the cabinet.
Q. Does the NEC permit splices, taps, and feed-through conductors in panelboards?
A. Yes, Sec. 312.8(A) permits splices, taps, and feed-through conductors in panelboards.
The wiring space within cabinets for panelboards can be used for conductors feeding through, spliced, or tapped where all the conditions of (1), (2), and (3) are met:
(1) The area of all conductors at any cross section does not exceed 40% of the cross-sectional area of that space (Fig. 1).
(2) The area of all conductors, splices, and taps installed at any cross section does not exceed 75% of the cross-sectional area of that space (Fig. 2).
Author’s Comment: The 40% and 75% requirements apply to all conductors, splices, and taps within the cross-sectional area, not just conductors, splice(s), or tap(s) being added.
(3) The bending space for conductors 4 AWG and larger complies with 314.28(A)(2).
(4) Where conductors feed through the cabinet, a permanently affixed warning label sufficiently durable to withstand the environment involved, and complying with 110.21(B), must be applied on the cabinet to identify the location of the disconnect for the feed-through conductors.