Code Q&A: Protection of Raceways and Cables in Wood Framing Members
Courtesy of www.MikeHolt.com
Based on the 2020 NEC.
Q. What are the Code rules relating to the protection of raceways and cables through wood members?
See answer below.
A. Holes through wood framing members for cables or raceways must be not less than 1¼ in. from the edge of the wood member. If the edge of a drilled hole in a wood framing member is less than 1¼ in. from the edge, a 1⁄16 in. thick steel plate of enough length and width must be installed to protect the wiring method from screws and nails [Sec. 300.4(A)(1)] (Figure).
Exception No. 1: A steel plate is not required to protect rigid metal conduit, intermediate metal conduit, PVC conduit, or electrical metallic tubing.
If notching of wood framing members for cables and raceways is permitted by the building code, a 1⁄16 in. thick steel plate of enough length and width must be installed to protect the wiring method laid in those wood notches from screws and nails [Sec. 300.3(A)(2)].
CAUTION: Many wood and metal framing members (especially joists and beams) have specific drilling and/or notching instructions meant to maintain structural integrity. Be sure to check with the building official for building code requirements.