Code Q&A: GFCI Protection Requirements at Carnivals, Circuses, and Fairs
Courtesy of www.MikeHolt.com
Based on the 2020 NEC.
Q. What are the Code requirements for GFCI protection of receptacles and equipment at carnivals, circuses, and fairs?
See answer below.
A. GFCI-Protected Receptacles and Equipment [Sec. 525.23(A)]
(A) GFCI Protection Required. In addition to the requirements of Sec. 210.8(B), GFCI protection must be provided for the following:
(1) 15A and 20A, 125V nonlocking‑type receptacles readily accessible to the general public or used for disassembly and reassembly of amusement rides and attractions.
(2) Equipment readily accessible to the general public if it is supplied from a 15A or 20A, 120V branch circuit.
GFCI protection can be integral with the attachment plug or located in the power‑supply cord within 12 in. of the attachment plug, or listed cord set incorporating GFCI protection.
These materials are provided to us by Mike Holt Enterprises in Leesburg, Fla. To view Code training materials offered by this company, visit www.mikeholt.com/code.