Figure. Each disconnecting means must be lockable in the open position per 110.25 [445.18].
Code Q&A: Standby Generator Requirements in Other Than Dwelling Units
April 13, 2022
Test your knowledge of the NEC.
Courtesy of www.MikeHolt.com
All questions and answers are based on the 2020 NEC.
Q. What are the Code rules for disconnecting means and emergency shutdown of standby generators, other than in one- and two-family dwelling units?
See answer below.
A. Follow these requirements as outlined in Sec. 445.18:
(A) Generators, other than cord-and-plug-connected portable generators, must have one or more disconnecting means. Each disconnecting means must simultaneously open all associated phase conductors. Each disconnecting means must be lockable in the open position per Sec. 110.25 [445.18] (Figure).
(B) Generators must have provisions to shut down the prime mover. The means of shutdown must comply with all the following:
(1) Be equipped with provisions to disable all prime mover start control circuits to render the prime mover incapable of starting.
(2) Initiate a shutdown mechanism that requires a mechanical reset. The provisions to shut down the prime mover are permitted to satisfy the requirements of Sec. 445.18(A) where it is capable of being locked in the open position per Sec. 110.25.
(C) Generators with a greater than 15kW rating must be provided with a remote emergency stop switch to shut down the prime mover. The remote emergency stop switch must be located outside the equipment room or generator enclosure and must also meet the requirements of Sec. 445.18(B)(1) and (B)(2).
Mike Holt