Www Ecmweb Com Sites Ecmweb com Files Uploads 2015 01 Ecm Mini Ad 2014
Code Q&A: AFCI Requirements
May 4, 2017
NEC rules on arc fault circuit interrupter protection
Q. Where is arc fault circuit interrupter protection required by the NEC?
Underlined text indicates a change in the rules for the 2017 NEC.
A. Arc fault circuit interrupter (AFCI) protection must be provided in accordance with Sec. 210.12(A), (B), and (C). AFCI devices must be installed in readily accessible locations.
(A) Required Locations. A listed combination AFCI breaker is required for all 15A or 20A, 120V branch circuits in dwelling units supplying outlets or devices in kitchens, family rooms, dining rooms, living rooms, parlors, libraries, dens, bedrooms, sunrooms, recreation rooms, closets, hallways, laundry areas, or similar rooms or areas.
(B) Dormitory Units. A listed combination AFCI breaker is required for all 15A or 20A, 120V branch circuits for outlets and devices in dormitory unit bedrooms, living rooms, hallways, closets, bathrooms, and similar rooms in accordance with Sec. 210.12(A).
(C) Guest Rooms and Guest Suites. A listed combination AFCI breaker is required for all 15A or 20A, 120V branch circuits supplying outlets and devices in guest rooms and guest suites of hotels and motels in accordance with Sec. 210.12(A).
(D) Branch‑Circuit Extensions or Modifications in Dwelling Units and Dormitory Units. Where 15A or 20A, 120V branch‑circuit wiring is modified, replaced, or extended in a dwelling unit or dormitory where AFCI protection is required [210.12(A)], the modified, replaced, or extended branch‑circuit wiring must be AFCI protected by one of the following methods:
(1) A listed combination AFCI circuit breaker
(2) A listed AFCI receptacle located at the first receptacle outlet of the branch circuit
Exception: AFCI protection isn’t required for extension wiring that’s less than 6 ft in length if no outlets or devices are added.