© Cheyennezj | Dreamstime.com
Dreamstime M 25829573 607de26215c0f
Chapter 9 of the NEC — Part 7
April 19, 2021
Tables at the end of Chapter 9 help when working with Art. 760.
Chapter 9 of the National Electrical Code (NEC) ends with a series of related tables:
  • 11(A). Class 2 and Class 3 Alternating Current Power Source Limitations.
  • 11(B). Class 2 and Class 3 Direct Current Power Source Limitations.
  • 12(A). Power Limited Fire Alarm (PLFA) Alternating Current Power Source Limitations.
  • 12(B). Power Limited Fire Alarm (PLFA) Direct Current Power Source Limitations.
When working with Art. 760, Part III, these are often helpful.
Inherently limited power supplies do not need overcurrent protection; that is often a reason to choose them. Suppose you have a 24VAC power supply inherently limited to 8A and its nameplate rating is 90A. Can you use it for your application that calls for a PLFA source? From Table 12(A), the answer is yes. What if your application calls for a Class 3 power supply? No, because Table 11(A) requires one over 30V.
In some cells, you see a figure such as 100/VMAX.. To know the quantity this represents, divide the numerator (top number) by the maximum voltage of the power supply. If the power supply maximum voltage is 50V, then 100/VMAX is 2.