mwilson_93/iStock/Getty Images Plus
outdoor decorative water fountain
NEC Rules for Pools, Tubs, Fountains, and Spas ― Part 2
Aug. 6, 2019
More highlights from Art. 680, Part II of the 2017 NEC
Article 680, Part II of the 2017 National Electrical Code (NEC) provides the requirements for electrical equipment associated with permanently installed pools. Some highlights include:
  • Areas where pool sanitation chemicals are stored and used are considered a corrosive environment [Sec. 680.14). In corrosive environments, wiring methods for motors must contain an insulated copper equipment grounding conductor (EGC) that complies with Table 250.122 and is at least 12AWG [Sec. 680.21(A)(1)].
  • In non-corrosive environments, the branch circuits must comply with the general requirements of Chapter 3.
  • Outlets connected to single-phase, 120V through 240V branch circuits and supplying pool pump motors must be GFCI-protected [Sec. 680.21(C)].
  • All metal fittings within or attached to the pool structure must be bonded [Sec. 680.26(B)(5). There is much more to the bonding requirements, so read all of them carefully. The point of them is to eliminate differences in potential between metallic objects, thus eliminating the shock hazard that would otherwise exist.
  • You'll read about “equipment grounding” requirements for underwater luminaires in Sec. 680.23(F)(2), but what is meant here isn't grounding. The EGC mentioned earlier is really a bonding jumper. See Art. 100 definitions.