Article 646 of the National Electrical Code (NEC) provides the requirements for everything in the modular data center enclosure, including the working space. Article 646 consists of four Parts, and Part IV is all about the workspace within a modular data center (and it takes up almost half a page).
The first concern is egress from the enclosure. The goal is to prevent trapping a person in there should a fire or another incident occur. That’s why, for example, the egress door(s) must open in the direction of egress and be equipped with panic bars, pressure plates, or other devices that are normally latched but open under simple pressure [Sec. 646.19].
Part IV also reflects concerns about working space around the IT equipment and batteries. Use Sec. 110.26 to determine that minimum working space.
The final concern is that workspace is sufficient to facilitate routine servicing and maintenance without exposing the worker to risk of electric shock or personal injury [Sec. 646.22]. This often requires exceeding the 110.26 minimums. Is there enough space to safely perform the maintenance tasks without, for example, risking back injury?