July 21, 2020
Key points of Art. 706
The requirements for energy storage systems were heavily changed with the 2020 National Electrical Code (NEC). That should come as no surprise, given the massive increase in large-scale wind and solar power generation systems. Article 706 provides the requirements for energy storage systems that have a capacity greater than 1kWh [706.1] and are capable of providing power to the premises wiring system or to a power distribution network [706.2].
Some key points include:
  • The disconnecting means must meet the requirements enumerated in 706.15(A)(1) through (3).
  • The disconnecting means must be installed per the requirements of Part III and 706.15(B) through (D).
  • Article 706 has its own requirements for conductor sizing [706.30], but you size overcurrent protection per Article 240 [706.31(A)].
  • Overcurrent protection devices for any dc portion must be listed for dc, and have the appropriate voltage, current, and interrupting rating for the application [706.31(C)].
  • The system must have provision for charge control. Adjustable means for control of the charging process must be accessible only to qualified personnel [706.33(A)].
  • A system using flow batteries must comply with Part V.