Article 445 contains installation and other requirements for generators.
The ampacity of the conductors from the generator terminals to the first distribution device containing overcurrent protection shall not be less than ____% of the nameplate rating of the generator.
a) 75
b) 115
c) 125
d) 140
See answer and applicable Code reference
The correct answer is: b) 115
Article 445 contains installation and other requirements for generators. As clearly noted in the first sentence of Sec. 445.13, "The ampacity of the conductors from the generator terminals to the first distribution device(s) containing overcurrent protection shall not be less than 115% of the nameplate current rating of the generator."