Question: Except as provided in Sec. 250.122(F)(2)(c) for raceway or cable tray installations, the equipment grounding conductor in each multiconductor cable shall be sized in accordance with Sec. 250.122 based on the _____.
a) largest circuit conductor
b) overcurrent protective device for the feeder or branch circuit
c) smallest branch-circuit conductor
d) overcurrent protective device for the service
See answer below.
Answer: b) overcurrent protective device for the feeder or branch circuit
Section 250.122(F)(2)(a) states, "Except as provided in 250.122(F)(2)(c) for raceway or cable tray installations, the equipment grounding conductor in each multiconductor cable shall be sized in accordance with 250.122 based on the overcurrent protective device for the feeder or branch circuit."