Fig. 1. PVC conduit is permitted to be installed within concealed locations such as walls, floors, or ceilings.
Stumped by the Code? NEC Requirements for Installing PVC
Nov. 9, 2023
Answering your NEC questions
Courtesy of www.MikeHolt.com
All questions and answers are based on the 2023 NEC.
Q: What are the conditions PVC can be used and installed?
A: As stated in Sec. 352.10, type PVC conduit is permitted in the following applications:
Note: In extreme cold, PVC conduit can become brittle and is more susceptible to physical damage.
(A) Concealed. PVC conduit can be concealed within walls, floors, or ceilings, as shown in Fig. 1 below.
(B) Corrosive Influences. PVC conduit is permitted in areas subject to severe corrosion for which the material is specifically approved by the authority having jurisdiction (AHJ).
(D) Wet Locations. PVC conduit is permitted in wet locations such as dairies, laundries, canneries, car washes, and other areas frequently washed. It is also permitted in outdoor locations. Support fittings such as straps, screws, and bolts must be made of corrosion-resistant materials or must be protected with a corrosion-resistant coating in accordance with Sec. 300.6(A).
(E) Dry and Damp Locations. PVC conduit is permitted in dry and damp locations except where limited in Sec. 352.12.
(F) Exposed. Schedule 40 PVC conduit is permitted for exposed locations where not subject to physical damage. If the conduit is exposed to physical damage, the raceway must be identified for the application. 
Note: PVC Schedule 80 conduit is identified for use in areas subject to physical damage. 
(G) Underground. PVC conduit is permitted to be installed underground and in concrete and must comply with the burial requirements of Sec. 300.5.
Q: Under what conditions can PVC not be used and installed?
A: Section 352.12 gives the conditions where PVC cannot be used and installed.
PVC conduit is not permitted in the following environments:
(A) Hazardous (Classified) Locations. PVC conduit is not permitted to be used in hazardous (classified) locations except as permitted by Sec. 501.10(A)(1)(a) Exception, Sec. 501.10(B)(6), Sec. 503.10(A), Sec. 504.20, Sec. 514.8 Exception No. 2, and Sec. 515.8.
(B) Support of Luminaires. PVC conduit is not permitted to be used for the support of luminaires or other equipment.
(C) Physical Damage. Type PVC conduit is not permitted to be installed where subject to physical damage unless identified for the application (see Fig. 2 below).
Author’s Comment: PVC Schedule 40 conduit is not identified for use where subject to physical damage, but PVC Schedule 80 conduit is [Sec. 352.10(F) Note].
(D) Ambient Temperature. PVC conduit is not permitted to be installed if the ambient temperature exceeds 50°C (122°F).
Author’s Comment: PVC conduit and fittings are not permitted to be installed in environmental air spaces (plenums) [Sec. 300.22(C)].
Q: What is the minimum and maximum PVC trade size permitted?
A: The minimum and maximum PVC trade size permitted is stated in Sec. 352.20.
(A) Minimum. PVC conduit smaller than trade size ½ is not permitted to be used.
(B) Maximum. PVC conduit larger than trade size 6 is not permitted to be used.
Mike Holt