Q. What are the requirements for securing and supporting RMC?

See answer below.

 

 

 

 

A. The requirements for securing and supporting RMC are in Sec. 344.30. 

RMC must be securely fastened in place and supported in accordance with (A) and (B).

(A) Securely Fastened. RMC must be secured in accordance with any of the following:

(1) Fastened within 3 ft of each outlet box, junction box, device box, cabinet, conduit body, or other conduit termination (Figure).

Author’s Comment: Fastening is required within 3 ft of terminations, not within 3 ft of each coupling.

(2) When structural members do not permit the raceway to be secured within 3 ft of a box or termination fitting, the raceway must be secured within 5 ft of the termination.

(3) Where approved, RMC is not required to be securely fastened within 3 ft of the service head for an above-the-roof termination of a mast. 

(B) Supports.

(1) General. RMC must be supported at intervals not exceeding 10 ft.

(2) Straight Runs. Straight runs made with threaded couplings can be supported in accordance with the distances contained in Table 344.30(B)(2).

(3) Vertical Risers. Exposed vertical risers for fixed equipment can be supported at intervals not exceeding 20 ft if the conduit is made up with threaded couplings, firmly supported, securely fastened at the top and bottom of the riser, and if no other means of support is available. 

(4) Horizontal Runs. Conduits installed horizontally in bored or punched holes in wood or metal framing members, or notches in wooden members are considered supported, but the raceway must be secured within 3 ft of termination.

Author’s Comment: RMC must be provided with expansion fittings where necessary to compensate for thermal expansion and contraction [300.7(B)]. The expansion characteristics for metal raceways are determined by multiplying the values from Table 352.44 by 0.20, and those for aluminum raceways are determined by multiplying the values from Table 352.44 by 0.40 [Sec. 300.7 Note].

These materials are provided to us by Mike Holt Enterprises in Leesburg, Fla. To view Code training materials offered by this company, visit www.mikeholt.com/code.

About the Author

Mike Holt

Mike Holt is the owner of Mike Holt Enterprises (www.MikeHolt.com), one of the largest electrical publishers in the United States. He earned a master's degree in the Business Administration Program (MBA) from the University of Miami. He earned his reputation as a National Electrical Code (NEC) expert by working his way up through the electrical trade. Formally a construction editor for two different trade publications, Mike started his career as an apprentice electrician and eventually became a master electrician, an electrical inspector, a contractor, and an educator. Mike has taught more than 1,000 classes on 30 different electrical-related subjects — ranging from alarm installations to exam preparation and voltage drop calculations. He continues to produce seminars, videos, books, and online training for the trade as well as contribute monthly Code content to EC&M magazine.

Voice your opinion!

To join the conversation, and become an exclusive member of EC&M, create an account today!

Sponsored Recommendations

How to Calculate Labor Costs

Most important to accurately estimating labor costs is knowing the approximate hours required for project completion. Learn how to calculate electrical labor cost.

8 Types of Electrical Conduit and Their Uses

Electrical conduit is a tube or raceway used to house and protect electrical wires within a building or structure. From data centers to underground subways to ports and bridges...

A Powerful Duo: Fiberglass conduit and solar applications

Learn how strong, durable fiberglass conduit excelled in an environment with dense cable and helped make a complex burial much simpler for the contractor to help this customer...

Champion Fiberglass® Conduit Protects Cabling For New York's First Offshore Wind Farm

Learn how fiberglass conduit supported a heavy cable load and a buried installation to help this project reach a successful outcome.