Q.  What is the NEC requirement for cables and conductors transitioning from a cable tray to a raceway?

See answer below.

A.  According to Sec. 392.46, a box is not required where cables or conductors are installed in a bushed raceway used for support, protection against physical damage, or where conductors or cables transition to a raceway from the cable tray (Figure).

(A) Through Bushed Conduit or Tubing. Individual conductors or multiconductor cables with entirely nonmetallic sheaths, can enter enclosures where they are terminated through nonflexible bushed conduit or tubing installed for their protection, provided they are secured at the point of transition from the cable tray and the raceway is sealed at the outer end using an approved means, so debris is prevented debris from entering the equipment through the raceway.

(B) Flanged Connections. Individual conductors or multiconductor cables with entirely nonmetallic sheaths can enter enclosures through openings associated with flanges from cable trays where the cable tray is attached to the flange and the flange is mounted directly to the equipment. The openings must be made so the conductors are protected from abrasion and must be sealed or covered to prevent debris from entering the enclosure through them.

Note: One method of preventing debris from entering the enclosure is to seal the outer end of the raceway or the opening with duct seal.

These materials are provided to us by Mike Holt Enterprises in Leesburg, Fla. To view Code training materials offered by this company, visit www.mikeholt.com/code.

About the Author

Mike Holt

Mike Holt is the owner of Mike Holt Enterprises (www.MikeHolt.com), one of the largest electrical publishers in the United States. He earned a master's degree in the Business Administration Program (MBA) from the University of Miami. He earned his reputation as a National Electrical Code (NEC) expert by working his way up through the electrical trade. Formally a construction editor for two different trade publications, Mike started his career as an apprentice electrician and eventually became a master electrician, an electrical inspector, a contractor, and an educator. Mike has taught more than 1,000 classes on 30 different electrical-related subjects — ranging from alarm installations to exam preparation and voltage drop calculations. He continues to produce seminars, videos, books, and online training for the trade as well as contribute monthly Code content to EC&M magazine.

Voice your opinion!

To join the conversation, and become an exclusive member of EC&M, create an account today!

Sponsored Recommendations

Electrical Conduit for Bridges Guide

Learn about electrical conduit for bridge projects.

Strut Comparison Chart

Conduit support systems are an integral part of construction infrastructure. Compare steel, aluminum and fiberglass strut support systems.

Considerations for Direct Burial Conduit

Installation type plays a key role in the type of conduit selected for electrical systems in industrial construction projects. Above ground, below ground, direct buried, encased...

Don't Let Corrosion Disrupt Your Next Project

The Complete Corrosion eGuide for Industrial Electrical Systems will help you avoid corrosion and its effects so you can spec for success for successful project outcomes.