Q.  What are the requirements for installing EMT couplings and connectors?
See answer below.
A.  According to Sec. 358.42 of the NEC, couplings and connectors must be made up tight in order to maintain an effective ground-fault current path to safely conduct fault current in accordance with Sec. 250.4(A)(5), 250.96(A), and 300.10.
If buried in masonry or concrete, threadless EMT fittings must be of the concrete-tight type. If installed in wet locations, they must be listed for use in wet locations and prevent moisture or water from entering or accumulating inside the enclosure in accordance with Sec. 314.15 (see Figure).