Fig. 1. Equipment grounding conductors must be sized not smaller than shown in Table 250.122; however, they are not required to be larger than the phase conductors.

The Differences Between Grounding and Bonding – Part 7 of 12

July 6, 2021
Do you know how to correctly size and install equipment grounding conductors?

Courtesy of www.MikeHolt.com.

This article is the seventh in a 12-part series on the differences between grounding and bonding.

Good workmanship is an NEC requirement [Sec. 110.12] that people often associate with how the completed work looks. But when you install an equipment grounding conductor (EGC), good workmanship includes more than just the things you can see when the work is complete. The fittings and terminations for raceways, cable trays, cable armor, cablebus framework, or cable sheaths must be made tight using suitable tools [Sec. 250.120(A)] and the correct methods.

Exposed EGCs 8 AWG and smaller for direct-current circuits [Sec. 250.134, Exception No .2], such as required by Sec. 690.45 for solar photovoltaic systems, can be run separately from the circuit conductors. Where the 8 AWG or smaller exposed EGC is subject to physical damage, it must be installed within an identified raceway or cable armor [Sec. 250.120(C)].

Aluminum and copper-clad aluminum EGCs

The requirements for EGCs that are bare, covered, or insulated aluminum and copper-clad aluminum are in Sec. 250.120(B).

You cannot install bare or covered aluminum or copper-clad aluminum conductors where subject to corrosive conditions or in direct contact with concrete, masonry, or earth, unless they are part of a suitable Chapter 3 wiring method.

Terminations made within outdoor enclosures that are listed and identified for the environment are permitted within 18 in. of the bottom of the enclosure. If open-bottom enclosures are installed on a concrete pad, the concrete is not considered earth.

Aluminum conductors external to buildings or enclosures cannot be terminated within 18 in. of the earth, unless terminated within a listed wire connector system.

Restricted use of EGCs

You can’t use an EGC as a grounding electrode conductor [Sec. 250.121(A)]. Exception: If an EGC meets the requirements for an EGC and grounding electrode conductor, you can use it as both an EGC and grounding electrode conductor.

You can’t use the structural metal frame of a building as an EGC [Sec. 250.121(B)]. Here is a perfect example of why it is so important you completely understand the terminology used throughout the Code: While the structural metal frame of a building can’t be used as an “EGC,” it can be used as a conductor to interconnect grounding electrodes [Sec. 250.68(C)(2)]. Knowing the difference is what makes the difference!

Sizing EGCs of the wire type

If your EGC is the raceway or cable tray containing the conductors (rather than a wire-type EGC), it will be larger than the phase conductors — and you don’t need to bother with the table. So, when we are talking about sizing EGCs, we mean wire-type EGCs. If you use both raceway and wire-type EGC enclosed within, the size requirements still apply to the wire-type EGC.

EGCs must be sized not smaller than shown in Table 250.122; however, the EGC is not required to be larger than the phase conductors [Sec. 250.122(A)] (Fig. 1 below). Phase conductors are sometimes increased in size to accommodate conductor voltage drop, shortcircuit rating, or future capacity. If phase conductors are increased in size for any reason other than as required in Sec. 310.15(B) or (C), wire-type EGCs, if installed, must be increased in size proportionately to the increase in the circular mil area of the phase conductors [Sec. 250.122(A)]. Exception: EGCs can be sized by a qualified person to provide an effective ground-fault current path per Sec. 250.4(A)(5) or (B)(4).

Example problem

Question: If the phase conductors for a 40A circuit (with 75ºC terminals) are increased in size from 8 AWG to 6 AWG due to voltage drop, the circuit EGC must be increased in size from 10 AWG to what?

Solution: The circular mil area of 6 AWG is 59% greater than 8 AWG (26,240cmil vs.16,510cmil) [Chapter 9, Table 8]. According to Table 250.122, the circuit EGC for a 40A overcurrent protective device will be 10 AWG (10,380cmil), but the circuit EGC for this circuit must be increased in size by a multiplier of 159%.

Conductor Size = 10,380cmil × 159% = 16,504cmil

Answer: Therefore, the circuit EGC must be increased in size to 8 AWG [Chapter 9, Table 8].

You can use a single EGC sized per Table 250.122 when multiple circuits are installed in the same raceway, cable, trench, or cable tray [Sec. 250.122(C)] (Fig. 2 below).

EGCs for motors

You must size EGCs for motor circuits per Sec. 250.122(D)(1) or (D)(2).

For motor circuits, follow Sec. 250.122(D)(1). The EGC must not be smaller than determined by Sec. 250.122(A), based on the rating of the motor circuit branch circuit shortcircuit and ground-fault protective device sized per Sec. 430.52(C)(1), Exception No. 1.

The EGC is not required to be larger than the motor circuit conductors [Sec. 250.122(A)].

Example problem

Question: What size EGC of the wire type is required for a 14 AWG motor branch circuit [Sec. 430.22], protected with a 2pole, 40A circuit breaker per Sec. 430.22 and Sec. 430.52(C)(1)?

Answer: The EGC is not required to be larger than the 14 AWG motor branch-circuit conductors [Sec. 250.122(D)(1) and Sec. 250.122(A)].

Parallel conductors

A 2020 revision has changed the requirements for when circuit conductors are installed in parallel per Sec. 310.10(G). If parallel circuit conductors are installed in:

  • a single nonmetallic raceway or cable tray, you must install a single wire-type EGC (sized per Table 250.122 based on the rating of the circuit overcurrent protective device) with the parallel circuit conductors [Sec. 250.122(F)(1)(a)].
  • multiple nonmetallic raceways, you must install a wire-type EGC in each raceway [Sec. 250.122(F)(1)(b)]. Size each one per Table 250.122 based on the rating of the circuit overcurrent protective device.

Example problem

Question: What size copper EGC of the wire type is required for a 4,000A feeder containing thirteen parallel sets of 500kcmil aluminum conductors per phase in PVC conduit?

Answer: According to Table 250.122, the copper EGC in each raceway must not be smaller than 500kcmil copper.

Cable trays and raceways

Wire-type EGCs installed in cable trays must meet the minimum requirements of Sec. 392.10(B)(1)(c) [Sec. 250.122(F)(1)(c)]. Metal raceways can serve as the required EGC per Sec. 250.118 and cable trays complying with Sec. 392.60(B) can serve as the required EGC. [Sec. 250.122(F)(1)(d)].

Parallel multiconductor cables

The EGC in each multiconductor cable must be sized per Sec. 250.122, based on the overcurrent protective device for the feeder or branch circuit [Sec. 250.122(F)(2)(a)] (Fig. 3 below).

If circuit conductors of multiconductor cables are connected in parallel, the EGC(s) in each cable must be connected in parallel [Sec. 250.122(F)(2)(b)].

If multiconductor cables are paralleled in the same raceway or cable tray, a single EGC sized per Sec. 250.122 is permitted in combination with the EGCs provided within the multiconductor cables and all EGCs must be connected [Sec. 250.122(F)(2)(c)].

EGCs installed in cable trays must meet the requirements of Sec. 392.10(B)(1)(c) [Sec. 250.122(F)(2)(d)]. Cable trays complying with Sec. 392.60(B) and metal raceways per Sec. 250.118 can be used as the required EGC.

Feeder tap conductors

EGCs for feeder taps are not permitted to be smaller than shown in Table 250.122, based on the ampere rating of the overcurrent device ahead of the feeder on the supply side of the tap [Sec. 250.122(G)]. The feeder EGC for the feeder tap is not required to be larger than the tap conductors.

Getting EGC size right

Before you start dealing with the EGC part of a project, take a moment to recognize that you’re not grounding anything. The “grounding” terminology is left over from when the NEC poorly defined terms related to bonding and grounding.

An EGC is actually an equipment bonding conductor. It forms a metallic path not to the earth (grounding, as defined in Art. 100) but back to the source. Recall that where a wire EGC is required, it’s run with the phase conductors instead of to a ground rod.

Because the EGC must be able to carry the fault current back to the source, its size matters. It matters relative to the current-carrying conductors. Whether you use the NEC tables to manually determine EGC sizes or a software program that automatically calculates EGC sizes, check to make sure the resulting numbers make sense.

These materials are provided to us by Mike Holt Enterprises in Leesburg, Fla. To view Code training materials offered by this company, visit www.mikeholt.com/code

About the Author

Mike Holt

Mike Holt is the owner of Mike Holt Enterprises (www.MikeHolt.com), one of the largest electrical publishers in the United States. He earned a master's degree in the Business Administration Program (MBA) from the University of Miami. He earned his reputation as a National Electrical Code (NEC) expert by working his way up through the electrical trade. Formally a construction editor for two different trade publications, Mike started his career as an apprentice electrician and eventually became a master electrician, an electrical inspector, a contractor, and an educator. Mike has taught more than 1,000 classes on 30 different electrical-related subjects — ranging from alarm installations to exam preparation and voltage drop calculations. He continues to produce seminars, videos, books, and online training for the trade as well as contribute monthly Code content to EC&M magazine.

Voice your opinion!

To join the conversation, and become an exclusive member of EC&M, create an account today!

Sponsored Recommendations

8 Types of Electrical Conduit and Their Uses

Electrical conduit is a tube or raceway used to house and protect electrical wires within a building or structure. From data centers to underground subways to ports and bridges...

A Powerful Duo: Fiberglass conduit and solar applications

Learn how strong, durable fiberglass conduit excelled in an environment with dense cable and helped make a complex burial much simpler for the contractor to help this customer...

Champion Fiberglass® Conduit Protects Cabling For New York's First Offshore Wind Farm

Learn how fiberglass conduit supported a heavy cable load and a buried installation to help this project reach a successful outcome.

How to Calculate Labor Costs

Most important to accurately estimating labor costs is knowing the approximate hours required for project completion. Learn how to calculate electrical labor cost.