• Emergency Systems and the NEC
    Emergency systems are lifelines for people, and Art. 700 is based on keeping those lifelines from breaking
    May 15, 2013
    8 min read
    Emergency systems are the circuits and equipment that supply illumination, power, or both within 10 sec [700.12] after interruption of the normal electrical supply [700.1] (Fig. 1). The requirements for the installation, operation, and maintenance of these systems are found in Art. 700.
    One use of emergency systems is to provide lighting for safely evacuating buildings that large numbers of people occupy (e.g., hospitals and sports arenas). These systems may also provide power to maintain life, fire detection and alarm systems, elevators, fire pumps, and public safety communications systems. They may even provide power to industrial processes to prevent the serious life safety or health hazards that would result from loss of power. But don’t confuse emergency systems with standby systems (see SIDEBAR: Standby Versus Emergency).
    Fig. 1. Article 700 applies to the installation, operation, and maintenance of emergency systems for illumination and/or power within 10 sec (700.12) of the interruption of the normal electrical supply.
    Testing and maintenance
    To ensure the emergency system meets or exceeds the original specifications, the AHJ must conduct or witness an acceptance test of the system after installation and before turnover to operations [700.3]. The initial testing also establishes baseline data for maintenance of the system and its components.
    The NEC requires periodic testing for maintenance. By “periodic,” the NEC means doing the testing at intervals recommended by the applicable standards, industry norms, and manufacturer literature. The AHJ refers to these to determine if the testing frequency is adequate.
    Load shedding
    The emergency system must be able to supply all emergency loads simultaneously [700.4(A)]. If an alternate power supply has adequate capacity, it may supply emergency loads [Art. 700], legally required standby loads [Art. 701], and optional standby system loads [Art. 702]. When the emergency supply also supplies power for nonemergency loads, the emergency loads take priority. If it doesn’t have adequate capacity to carry all loads, it must have automatic selective load pickup and load shedding to ensure adequate power in this order of priority [700.12(B)]:
    1) Emergency circuits
    2) Legally required standby circuits
    3) Optional standby circuits
    A temporary alternate source of power must be available whenever the emergency generator is out of service for more than a few hours for maintenance or repair.
    Transfer equipment
    Transfer equipment must be automatic, identified for emergency use, and approved by the AHJ [700.5 (A)]. It must supply only emergency loads (Fig. 2). Automatic transfer switches must be electrically operated, mechanically held, and listed for emergency system use. You must use multiple transfer switches where a single generator supplies emergency loads plus other loads.
    Fig. 2. The alternate power source is permitted to supply other loads in addition to emergency loads; however, the transfer switch for emergency loads can only supply emergency loads.
    Wiring
    At the service-entrance equipment, place a sign indicating the type and location of on-site emergency power sources [700.7]. Permanently mark the system’s boxes and enclosures as components of an emergency system [700.10(A)]. That requirement includes transfer switches, generators, and power panels for emergency circuits.
    To ensure that a fault on the normal wiring circuits won’t affect the performance of emergency wiring or equipment, keep all wiring to emergency loads independent of all other wiring. These exceptions apply to:
    Fig. 3. To ensure a fault on the normal wiring circuits won’t affect the performance of emergency wiring or equipment, keep all wiring to emergency loads independent of all other wiring, except for wiring in transfer equipment.
    • Wiring in transfer equipment (Fig. 3).
    • Luminaires supplied from two sources of power.
    • A junction box attached to luminaires supplied from two sources of power.
    • Wiring within a common junction box attached to unit equipment, containing only the branch circuit supplying the unit equipment and the emergency circuit supplied by the unit equipment.
    Wiring from an emergency source can supply any combination of emergency, legally required, or optional standby loads — but only under one of these conditions [710(B)(5)]:
    • It’s supplied from separate vertical switchboard sections or from individual disconnects mounted in separate enclosures.
    • It’s supplied from single or multiple feeders without overcurrent protection at the source. You can provide overcurrent protection at the source (or for the equipment), if the overcurrent protection is selectively coordinated with the downstream overcurrent protection.
    • The legally required and optional standby circuits don’t originate from the same vertical switchboard section, panelboard enclosure, or individual disconnect enclosure as emergency circuits.
    How can you accomplish separation of the circuits served by a generator source for emergency, legally required, and optional standby circuits? By running feeders from a single generator to individual overcurrent devices or to a distribution switchboard that separates emergency circuits in different vertical sections from other loads.
    Design and locate emergency wiring circuits so as to minimize the hazards that might cause failure due to flooding, fire, icing, vandalism, and other adverse conditions [700.10(C)].
    Power sources
    You have six choices for the emergency power supply:
    1) Storage battery
    2) Generator set
    3) UPS
    4) Separate service
    5) Fuel cell
    6) Individual unit equipment
    Storage batteries must be of suitable rating and capacity to supply and maintain the total load for 1½ hr, without the voltage applied to the load falling below 87½% of normal [700.12(A)].
    A generator set can be any of several configurations. If it’s prime mover-driven, it must be:
    • Approved by the AHJ.
    • Sized per 700.5.
    • Able to automatically start the prime mover when the normal service fails.
    If you use internal combustion engines as the prime mover, provide an on-site fuel supply sized for at least 2 hr of full-demand operation [700.12(B)(2)].
    If an outdoor generator has a readily accessible disconnecting means within sight of the structure, you don’t need an additional disconnecting means (on or at the structure) for the generator feeder conductors that serve or pass through the structure.
    You don’t need to locate the generator disconnecting means within sight of the structure served, if you satisfy these two requirements:
    1) Conditions of maintenance and supervision ensure that only qualified persons will monitor and service the installation.
    2) Documented safe switching procedures are established and maintained for disconnection.
    A UPS serving as the emergency power source must comply with the applicable requirements for batteries and generators.
    By individual unit equipment (IUE), the NEC means an emergency lighting battery pack [700.12(F)]. These are traditionally shaped much like a lunchbox, and thus are sometimes called “lunchboxes” in the field. They must include (Fig. 4):
    Fig. 4. The battery-powered emergency light must contain a relay device to automatically energize the lamp when there’s loss of power to the unit.
    1) Rechargeable battery,
    2) Battery charging means,
    3) Provisions for one or more lamps mounted on the equipment, or terminals for remote lamps (or both),
    4) Relaying device that energizes the lamps automatically upon failure of the supply to the unit.
    IUE must be permanently fixed in place. A locking receptacle is optional. You can use a flexible cord and plug connection for IUE designed for this purpose, if the cord doesn’t exceed 3 ft.
    The branch circuit wiring that supplies IUE must be the same branch-circuit wiring that supplies the normal lighting in the area. Don’t connect IUE to the emergency circuit. It won’t operate upon loss of normal power, because it will still have power.
    Connect the IUE ahead of any local switches. The branch circuit that feeds the IUE must be clearly identified at the distribution panel per 110.22(A) and 408.4.
    Emergency lighting systems must be designed and installed so that the failure of any individual lighting element, such as the burning out of a lamp, won’t leave any space that requires emergency illumination [700.16] in total darkness. So a single remote head is never sufficient. This is why you always see two lighting heads on IUE boxes.
    Overcurrent protection
    The branch circuit overcurrent devices for emergency circuits must be accessible to authorized persons only [700.25]. You don’t have to GFCI protect the alternate power supply for emergency systems. But 700.7(D) requires ground fault indication of the emergency power supply. Overcurrent devices for emergency systems must be selectively coordinated with all supply-side overcurrent devices [700.27]. With selective coordination, the overcurrent protection scheme confines the interruption to a particular area. For example, if a short circuit or ground fault occurs with selective coordination, the only breaker/fuse that will open is the one protecting that branch circuit. The local fault won’t bring down the feeder or whole system.
    Holt is the owner of Mike Holt Enterprises, Inc. in Leesburg, Fla. He can be reached at www.mikeholt.com.
    A standby system automatically provides power to critical equipment if normal power is interrupted. Standby systems may be optional (Art. 702) or legally required (Art. 701). A glass plant, for example, would want a standby system so that molten glass doesn’t solidify in the equipment and thus destroy it. A chemical plant might be legally required to power systems that prevent an environmental release or a runaway reaction.
    Emergency systems are legally required and classed as emergency by a governmental agency having jurisdiction. These systems automatically supply illumination and/or power essential for safety to human life.
    Sometimes, an emergency system simply provides power for exit lighting and exit signs upon loss of the main power or in the case of fire. Its purpose isn’t to provide power for normal business operations, but rather to provide lighting and controls essential for egress to a safe area.
    Mike Holt