Figure. A conduit seal fitting must be installed in each raceway that enters an explosionproof enclosure that contains make-and-break contacts

Code Q&A: Raceway and Cable Seals in Class I Locations

June 22, 2022
Test your knowledge of the NEC.

Courtesy of www.MikeHolt.com

All questions and answers are based on the 2020 NEC.

Q. What does the Code require for raceway and cable seals in Class I locations?

See answer below.

A. Seals for raceway and cable systems must comply with Sec. 501.15(A) through (F) [Sec. 501.15].

Note 1: Raceway and cable seals must be installed to: 

  • Minimize the passage of gases and vapors from one portion of electrical equipment to another through the raceway or cable.
  • Minimize the passage of flames from one portion of electrical equipment to another through the raceway or cable.
  • Limit internal explosions to within the explosionproof enclosure.

(A) Raceway Seal — Class I, Division 1. In Class I, Division 1 locations, raceway seals must be located as follows:

(1) Entering Enclosures. A raceway seal is required in each raceway that enters an explosionproof enclosure if either (1) or (2) apply:

(1) If the explosionproof enclosure contains make-and-break contacts (Figure).

Exception: A raceway seal is not required if the make-and-break contacts are:

(1) Within a hermetically sealed chamber. 

(2) Immersed in oil in accordance with Sec. 501.115(B)(1)(2).

(3) Contained within an enclosure that is marked “Leads Factory Sealed,” “Factory Sealed,” “Seal not Required,” or the equivalent.

These materials are provided to us by Mike Holt Enterprises in Leesburg, Fla. To view Code training materials offered by this company, visit www.mikeholt.com/code.

About the Author

Mike Holt

Mike Holt is the owner of Mike Holt Enterprises (www.MikeHolt.com), one of the largest electrical publishers in the United States. He earned a master's degree in the Business Administration Program (MBA) from the University of Miami. He earned his reputation as a National Electrical Code (NEC) expert by working his way up through the electrical trade. Formally a construction editor for two different trade publications, Mike started his career as an apprentice electrician and eventually became a master electrician, an electrical inspector, a contractor, and an educator. Mike has taught more than 1,000 classes on 30 different electrical-related subjects — ranging from alarm installations to exam preparation and voltage drop calculations. He continues to produce seminars, videos, books, and online training for the trade as well as contribute monthly Code content to EC&M magazine.

Voice your opinion!

To join the conversation, and become an exclusive member of EC&M, create an account today!

Sponsored Recommendations

Latest from Q&A

ID 360841573 © Kenishirotie | Dreamstime.com
dreamstime_xl_360841573
ID 342911317 © May1985 | Dreamstime.com
dreamstime_xxl_342911317
ID 355536544 © Tatsiana Kuryanovich | Dreamstime.com
dreamstime_xxl_355536544

Sponsored