350 10 01 Ph 61152af62e054
Code Q&A: Permitted Uses of LFMC
Aug. 12, 2021
Test your Code knowledge.
Q. What are the uses permitted by the NEC for Type LFMC?
See answer below.
A. Listed LFMC is permitted, either exposed or concealed, at any of the following locations (Sec. 350.10):
(1) If flexibility or protection from machine oils, liquids, vapors, or solids is required.
(2) In hazardous locations as permitted in Chapter 5.
(3) For direct burial, if listed and marked for this purpose.
(4) Conductors or cables rated at a temperature higher than the listed temperature rating of LFMC may be installed in LFMC, provided the conductors or cables are not operated at a temperature higher than the listed temperature rating of the LFMC per Sec. 110.14(C).