Code Q&A
Code Q&A: Supplementary Overcurrent Protection Rules
Jan. 10, 2019
Here's a refresher on where you can and can't use supplemental overcurrent protection devices.
Q. What is the NEC rule for the use of supplementary overcurrent protection?
See the answer below.
This answer is based on the 2017 NEC.
A. Supplementary overcurrent protection devices aren’t permitted to be used as the required branch-circuit overcurrent protection device [Sec. 240.10]. A supplementary overcurrent protection device isn’t required to be readily accessible.
Article 100 defines a “Supplementary Overcurrent Protection Device” as a device intended to provide limited overcurrent protection for specific applications and utilization equipment. This limited overcurrent protection is in addition to the overcurrent protection provided in the required branch circuit by the branch-circuit overcurrent protection device. See Sec. 240.24(A)(2) for requirements regarding overcurrent protection devices that are not intended for supplemental use.
These materials are provided to us by Mike Holt Enterprises in Leesburg, Fla. To view Code training materials offered by this company, visit www.mikeholt.com/code