Code Q&A Mike Holt
Code Q&A: Surface Extensions
July 5, 2018
Q. What is the Code rule regarding the installation of surface extensions from a box or box cover?
See the answer below.
This answer is based on the 2017 NEC.
A. Surface extensions can only be made from an extension ring installed over a box [Sec. 314.22].  
Exception: A surface extension can be made from the cover of a box if the cover is designed so it’s unlikely to fall off if the mounting screws become loose. The surface extension wiring method must be flexible to permit the removal of the cover and provide access to the box interior, and equipment grounding continuity must be independent of the connection between the box and the cover.
These materials are provided to us by Mike Holt Enterprises in Leesburg, Fla. To view Code training materials offered by this company, visit www.mikeholt.com/code.