Q. What are the rules in sizing a supply side bonding jumper sized for a single raceway containing service conductors?
Find the Answer
A. The supply-side bonding jumper (SSBJ) at a service ensures the required electrical conductivity between metal parts required to be connected [Art. 100 definition]. In single raceway installations, the supply-side bonding jumper is sized in accordance with Table 250.102(C)(1) of the 2014 NEC, based on the largest ungrounded conductor within the raceway [250.102(C)(1)], as shown in the Figure.