Code Q&A: Rules When Mixing Conductor Types in Same Raceway
June 11, 2015
NEC rules on installation of conductors
Q. What are the rules related to the installation of conductors under 50V with conductors from 120V, 208V, 240V, 277V, and 480V systems in the same raceway or enclosure?
A. Class 1 circuit conductors can be installed with associated power conductors [725.48(B)(1)] if all conductors have an insulation voltage rating not less than the maximum circuit voltage [300.3(C)(1)]. A Class 2 circuit that’s been reclassified as a Class 1 circuit [725.130(A), Exception No. 2] can be installed with associated power conductors [725.48(B)(1)] if all conductors have an insulation voltage rating not less than the maximum circuit voltage [300.3(C)(1)] (Figure).
Control, signal, and communications wiring must be separated from power and lighting circuits so the higher-voltage conductors don’t accidentally energize the control, signal, or communications wiring.
Note 2: PV system conductors, both direct current and alternating current, are permitted to be installed in the same raceways, outlet and junction boxes, or similar fittings with each other, but they must be kept entirely independent of all other non-PV system wiring [690.31(B)].