Q. How do we size the conductors and maximum overcurrent protection for an electric water heater? Please give an example.

A. An electric water heater having a capacity of 120 gal or less is considered a continuous load, for the purpose of sizing branch circuits [422.13]. Branch circuit conductors must have a rating of at least 125% of the ampere rating of a continuous load [422.10] and the overcurrent protection is sized to the requirements in Sec. 422.11(E)(3).

Branch circuit conductors must have overcurrent protection in accordance with Sec. 240.4, and the overcurrent device rating must not exceed the rating marked on the appliance [422.11(A)]. A typical water heater is considered a single non-motor-operated appliance and many of these don’t have a marked overcurrent protection size. For non-motor appliances, the appliance overcurrent device must [422.11(E)]:

1) Not exceed the rating marked on the appliance, if not marked.

2) Not exceed 20A if the overcurrent device rating isn’t marked, and the appliance is rated 13.30A or less, or

3) Not exceed 150% of the appliance rated current if the overcurrent device rating isn’t marked, and the appliance is rated over 13.30A. Where 150% of the appliance rating doesn’t correspond to a standard overcurrent device ampere rating listed in Sec. 240.6(A), the next higher standard rating is permitted.

Fig. 1. Size an overcurrent protection device for a water heater per the steps noted in this figure.

Let’s run through an example now to drive these points home.

What’s the maximum size overcurrent protection device for a 4,500W, 240V water heater (Fig. 1)?

Protection Size = 4,500W ÷ 240V = 18.75A × 1.50 = 28A

Looking to the next size up, we would choose a 30A device [240.6(A)].

Size the branch circuit conductors at 125% [422.10(A)].

Conductor Size = 18.75A × 1.25 = 23.4A

Referring to Table 310.15(B)(16), we see a 10 AWG conductor is rated 30A at 60°C.

Section 240.4(D)(7) required a 30A protection device for 10 AWG. Section 110.14(C)(1)(a)(1) directs us to the 60°C column of Table 310.15(B)(16) to match conductor sizing to terminal ratings.

Q. When is an on-site generator not a separately derived system?

A. An alternating-current power source such as an on-site generator isn’t a separately derived system if the neutral conductor is solidly interconnected to a service-supplied system neutral conductor. An example is a generator provided with a transfer switch that includes a neutral conductor that’s not switched [250.30 Note 1], as shown in Fig. 2.

Fig. 2. See Art. 100 for a definition of a separately derived system.

According to Art. 100, a separately derived system is a wiring system whose power is derived from a source, other than a utility, where there’s no direct electrical connection to the supply conductors of another system, other than through grounding and bonding connections.

Transformers are separately derived when the primary conductors have no direct electrical connection from circuit conductors of one system to circuit conductors of another system, other than connections through grounding and bonding connections.

A generator having transfer equipment that switches the neutral conductor, or one that has no neutral conductor at all, is a separately derived system and must be grounded and bonded in accordance with Sec. 250.30(A).

For non-separately derived systems, see Sec. 445.13 for the minimum size neutral conductors necessary to carry fault current [250.30 Note 2].

Q. What are the rules for sizing an equipment bonding jumper sized for parallel feeder circuits in a raceway?

A. Bonding jumpers on the load side of feeder and branch circuit overcurrent devices are sized in accordance with Sec. 250.122, based on the rating of the circuit overcurrent device [250.102(D)]. For example, let’s say you’re working with metal raceway where the circuit conductors are protected by a 1,200A overcurrent device. A quick check of Table 250.122 reveals the minimum size bonding jumper needed is 3/0 AWG. It’s also important to note that if a single bonding jumper is used to bond two or more raceways, it must be sized in accordance with Sec. 250.122, based on the rating of the largest circuit overcurrent device.    

About the Author

Mike Holt

Mike Holt is the owner of Mike Holt Enterprises (www.MikeHolt.com), one of the largest electrical publishers in the United States. He earned a master's degree in the Business Administration Program (MBA) from the University of Miami. He earned his reputation as a National Electrical Code (NEC) expert by working his way up through the electrical trade. Formally a construction editor for two different trade publications, Mike started his career as an apprentice electrician and eventually became a master electrician, an electrical inspector, a contractor, and an educator. Mike has taught more than 1,000 classes on 30 different electrical-related subjects — ranging from alarm installations to exam preparation and voltage drop calculations. He continues to produce seminars, videos, books, and online training for the trade as well as contribute monthly Code content to EC&M magazine.

Voice your opinion!

To join the conversation, and become an exclusive member of EC&M, create an account today!

Sponsored Recommendations

Latest from Q&A

ID 57245818 © Mrchan | Dreamstime.com
dreamstime_xl_57245818
ID 360841573 © Kenishirotie | Dreamstime.com
dreamstime_xl_360841573
ID 342911317 © May1985 | Dreamstime.com
dreamstime_xxl_342911317

Sponsored