Image

Code Quandaries

May 1, 2008
What are the requirements for installing isolated ground receptacles?

All questions and answers are based on the 2008 NEC.

Q. What are the requirements for installing isolated ground receptacles?

A. The grounding terminal of an isolated ground receptacle must be connected to an insulated equipment-grounding conductor run with the circuit conductors [250.146(D)], as shown in the Figure. The circuit equipment-grounding conductor is permitted to terminate to the panelboard supplying the power, or it is permitted to pass through the panelboard [408.40 Ex], boxes, wireways, or other enclosures [250.148 Ex] without a connection to the enclosure — as long as it terminates at an equipment-grounding conductor terminal of the derived system or service.

Q. Are you required to pre-twist conductors before installing a twist-on wire connector?

A. Maybe. As per 110.3(B), all electrical products are required to be installed in accordance with equipment instructions. According to the UL “White Book” (product category ZMVV), “some connectors may specify that conductors are to be pre-twisted before assembly onto the connector.”

Q. Can the service disconnecting means for a building be located inside the building?

A. The service disconnecting means must be placed at a readily accessible location either outside the building or structure, or inside nearest the point of service conductor entry [230.70(A)(1)]. Because service-entrance conductors don't have short-circuit or ground-fault protection, they must be limited in length when installed inside a building. Some local jurisdictions have a specific requirement as to the maximum length permitted within a building.

Q. What are the rules for placing overhead service conductors above a swimming pool?

A. Permanently installed pools, storable pools, outdoor spas, outdoor hot tubs, fountains, diving structures, observation stands, towers, or platforms must not be placed within the clearances contained in Table 680.8. This rule doesn't prohibit utility-owned overhead service-drop conductors from being installed over a permanently installed pool, storable pool, outdoor spa, outdoor hot tub, or fountain [90.2(B)(5)]. It does prohibit a permanently installed pool, storable pool, outdoor spa, outdoor hot tub, or fountain from being installed under an existing service drop that isn't at least 22.5 feet above the water.

Q. We have motors that are interlocked, preventing them from being on at the same time. Do we still have to add them up for our service and feeder calculations?

A. No. Where the circuitry is interlocked to prevent operation of motors at the same time, only those motors that operate simultaneously (and result in the largest current) need to be counted [430.24 Ex No. 3].

Q. Where must I install the disconnecting means for a remote building?

A. The disconnecting means for a remote building must be installed at a readily accessible location at the building (outside or inside) nearest the point of entrance of the conductors [225.32].

Q. Am I required to identify the raceways and enclosures in an emergency system?

A. Only the boxes and enclosures (including transfer switches, generators, and power panels) for emergency circuits must be permanently marked as components of an emergency system [700.9(A)]. The Code doesn't require raceways to be identified as a component of an emergency system.

Q. Does the Code allow equipment rooms containing overcurrent devices to be locked? What about locking panel covers and disconnecting means?

A. Yes, electrical equipment rooms and enclosures housing electrical equipment or apparatus can be locked [110.26(G)].

Q. Does the NEC require GFCI protection for a 15A/125V receptacle in a basement for a sump pump?

A. Yes. It is required for all 15A and 20A, 125V receptacles located in the unfinished portion of a basement not intended as a habitable room and limited to storage and work areas [210.8(A)(5)].

About the Author

Mike Holt

Mike Holt is the owner of Mike Holt Enterprises (www.MikeHolt.com), one of the largest electrical publishers in the United States. He earned a master's degree in the Business Administration Program (MBA) from the University of Miami. He earned his reputation as a National Electrical Code (NEC) expert by working his way up through the electrical trade. Formally a construction editor for two different trade publications, Mike started his career as an apprentice electrician and eventually became a master electrician, an electrical inspector, a contractor, and an educator. Mike has taught more than 1,000 classes on 30 different electrical-related subjects — ranging from alarm installations to exam preparation and voltage drop calculations. He continues to produce seminars, videos, books, and online training for the trade as well as contribute monthly Code content to EC&M magazine.

Voice your opinion!

To join the conversation, and become an exclusive member of EC&M, create an account today!

Sponsored Recommendations

Latest from Q&A

ID 360841573 © Kenishirotie | Dreamstime.com
dreamstime_xl_360841573
ID 342911317 © May1985 | Dreamstime.com
dreamstime_xxl_342911317
ID 355536544 © Tatsiana Kuryanovich | Dreamstime.com
dreamstime_xxl_355536544

Sponsored