alexsl/iStock/Getty Images Plus
Pv Alexsl I Stock Getty Images Plus 5df7f1a5daac1
Photovoltaic Systems — Part 2
Dec. 16, 2019
The ins and outs of electrical requirements for PV installations from Art. 690.
The circuit requirement for photovoltaic (PV) systems are covered in Part II of the 2017 National Electrical Code (NEC). To correctly size the overcurrent protection [Sec. 690.9] and conductors, you must first determine the maximum voltage [Sec. 690.7] and the maximum current [Sec. 690.8].
The maximum voltage of any PC system is the highest voltage between any two circuit conductors or any circuit conductor and ground [Sec. 690.7]. While this sounds straightforward enough, there's a three-step calculation process for the PV source and output circuits. But if you have a single DC-to-DC converter the maximum rated voltage of the system is the maximum rated voltage of that converter. If you have more than one converter (series connected), instructions for calculating the maximum rated voltage come with the converters.
You can calculate the maximum current by one of two methods:
  1. Sum up all the parallel-connected PV module-rated short circuit currents, then multiply by 125%.
  2. For systems that can generate 100kW or more, you can base it on the highest 3-hour current average resulting from the simulated local irradiance, accounting for elevation and orientation. This requires a PE stamp.