Part II of Art. 550 in the 2017 NEC provides the requirements for the power supply to these structures
Part II of Art. 550 in the 2017 Edition of the National Electrical Code (NEC) provides the requirements for the power supply to these structures. Services and feeders to them are covered separately in Part III of Art. 550.
One requirement is the mobile home park secondary electrical system to mobile home lots must be single-phase, 120/240V [Sec. 550.30]. So, home service equipment is going to be for that type of distribution. And the service must be rated at least 100A [Sec. 550.32(C)].
Service equipment cannot be mounted on or in a mobile home [Sec. 550.32(A)], but it can be mounted on or in a manufactured home if the conditions of Sec. 550.32(B)(1) through (7) are met.
What if you have a car port or little tool shed to supply power to? You must use a fixed wiring method in either the service equipment or the local external disconnecting means that Sec. 550.32(A) permits [Sec. 550.32(D)]. You can’t run it from the breaker panel inside the unit.
Feeder conductor installation must comply with Sec. 250.32B (one exception is noted) [Sec. 550.33]. Feeder capacity must be at least equal to the loads supplied [Sec. 550.33(B)].