Stumped by the Code? Rules for Multiple Type MC Cables Installed in Contact with Thermal Insulation
Courtesy of www.MikeHolt.com.
All questions and answers are based on the 2020 NEC.
Q. What does the Code require when multiple Type MC cables are installed in contact with thermal insulation?
A. Where more than two Type MC cables are installed in contact with thermal insulation or pass through the same wood framing opening that is to be sealed with thermal insulation, caulking, or sealing foam, the ampacity of each conductor must be adjusted in accordance with Table 310.15(C)(1) [Sec. 330.80(C)] (Fig. 1 below).
Q. What is the maximum cable length allowed by the NEC between the cable entry of Type NM cable into cabinets and enclosures and the closest cable support?
A. Type NM cable must be supported and secured by staples or straps; cable ties listed and identified for securing and supporting; hangers, or similar fittings, at intervals not exceeding 4½ ft and within 12 in. of every cable entry termination. The cable length between the cable entry termination and the closest cable support must not exceed 18 in. [Sec. 334.30] (Fig. 2 below).
Author’s comment: Many times, there is a tendency to leave a length of sheathed NM cable in a box or enclosure (such as a panelboard) just to have “extra” cable. While this practice is not prohibited, the length of such sheathed cable cannot exceed 18 in. as measured in a straight line.
Q. In one-and two-family dwellings, Type TC-ER-JP cable is permitted by the Code for what type of use?
A. Per Sec. 336.10(9), Type TC-ER-JP cable is permitted to be used in one- and two-family dwellings for branch circuits and feeders, where installed in accordance with Part II of Art. 334 for interior wiring and Part II of Art. 340 for exterior wiring.
Author’s comment: The “ER” marking on Type TC‑ER cable identifies it as suitable for exposed run use in accordance with UL 1277 and the suffix “-JP” identifies it as being suitable for pulling through framing members.
Exception: Where Type TC cable is used to connect a generator and its associated equipment, the cable ampacity limitations of Sec. 334.80 and Sec. 340.80 do not apply.
These materials are provided to us by Mike Holt Enterprises in Leesburg, Fla. To view Code training materials offered by this company, visit www.mikeholt.com/code.