Article 440 focuses on air-conditioning and refrigeration equipment. More specifically, Section 440.14 deals with the location of the disconnection means. The requirement reads as follows:
"Disconnecting means shall be located within sight from and readily accessible from the air-conditioning or refrigerating equipment. The disconnecting means shall be permitted to be installed on or within the air-conditioning or refrigerating equipment.
"The disconnecting means shall not be located on panels that are designed to allow access to the air-conditioning or refrigeration equipment or to obscure the equipment nameplate(s).
"Exception No. 1: Where the disconnecting means provided in accordance with 430.102(A) is capable of being locked in the open position, and the refrigerating or air-conditioning equipment is essential to an industrial process in a facility with written safety procedures, and where the conditions of maintenance and supervision ensure that only qualified persons service the equipment, a disconnecting means within sight from the equipment shall not be required. The provision for locking or adding a lock to the disconnecting means shall be installed on or at the switch or circuit breaker and shall remain in place with or without the lock installed.
"Exception No. 2: Where an attachment plug and receptacle serve as the disconnecting means in accordance with 440.13, their location shall be accessible but shall not be required to be readily accessible.
"FPN: See Parts VII and IX of Article 430 for additional requirements."
> Try Another Quiz
Discuss this Article 0
Post new comment
Sign In or register to use your Electrical Construction & Maintenance (EC&M) Magazine ID
(optional)
White Papers
EC&M Learning Center
Webinars
EC&M TV
Apr. 15, 2013
video
Protection From Arc Flashes
Learn how arc flashes happen, how they are measured and how wearing the right flame resistant clothing can keep workers safe....More
Newsletter Signup
Connect With Us