What is in this article?:
- What's Wrong Here?
- Find the Answer
How well do you know the Code? Think you can spot violations the original installer either ignored or couldn't identify? Here's your chance to moonlight as an electrical inspector and second-guess someone else's work from the safety of your living room or office. Joe Tedesco, who has a knack for finding shoddy electrical work, did the dirty work and found this mess. Now it's your turn to identify
Answer:
Rebecca Ashley, an electrical engineer with Henderson Mill in Parshall, Colo., cited the following sections of the Code when reviewing the February photograph.
“110.3(A)(1) — This equipment is not listed for this application.
“110.3(A)(4) — Duct tape being used to insulate the conductors is not acceptable.
“110.3(A)(7) — This receptacle is not classified for this use.
“110.3(A)(8) — This application is not safe for persons coming in contact with this equipment.
“110.3(B) — This equipment is not listed and labeled for this use (UL 498).
“590.6(A) — A GFCI would be a lifesaver in this application, either tripping because of the moisture or when the user completed the circuit.
“406.4 — Receptacles shall be mounted in boxes or assemblies designed for the purpose.”
David Furi, a master electrician/foreman with Lakepointe Electric in Sterling Heights, Mich., added this to the mix. “It appears that someone has removed the receptacle end of an extension cord set and replaced it with a grounding type duplex receptacle and insulated it with duct tape. The violation is under the 2005 NEC Sec. 590.6(B)(2)(a). It is also an OSHA violation because this cord set should have been tagged and removed from service on the job site.”
Joel Van Ravenswaay, an electrician at Grand Valley State University in Allendale, Mich., injected some humor into his response. “It looks like the ground isn't moist enough to efficiently grow outlets from seed! Or it could be violations of….
“406.8 — receptacles placed in damp or wet locations need a box that meets the environment.
“210.8 — need GFCI protection, assuming this is an outside installation.
“590.4 — Temporary installations…. This is most likely the culprit, a cutoff extension cord on a construction site for temp power.
“But it looks like there are remnants of duct tape in the dirt, so give them some credit. If you can't do it right, duct tape it!”
