What’s Wrong Here? Hint: You're Not on the List!
Discuss this Article 11
mulwee (not verified)
on Jan 16, 2013
The mc cable is supported by cable ties, attatched to the conduit. That is a code violation.
Anonymous (not verified)
on Jan 17, 2013
he is correct by saying that the securing method used of plastic ties are not code
on Jan 17, 2013
That metal cable does not look to be suitable for electric. It looks like a gooseneck for microphones. I doubt if it's UL listed.
mrsafetyman
on Jan 17, 2013
Right EMT not properly supported by a strap 36" from box or termination. MC/FMC is not allowed to be strapped to the EMT also communications cables or wires shall not be strapped, taped, or attached by any means to the exterior of conduit or raceway as a means of support."
mrsafetyman
on Jan 17, 2013
OK the first picture did not show the full length of the PICTURE. 1st picture only shows about 4 foot of MC or FMC
on Jan 18, 2013
agreed, I wish they would show the full picture right away. Not try and hide things.
on Jan 17, 2013
300.11(B)
stewie52
on Jan 21, 2013
cannot see all of the emt so it may not be properly supported .
mike fisher (not verified)
on Jan 26, 2013
cable ties are not an approved method to strap, and it appears the emt that it is strapped to has a coupling, wich would mean it is probably not properly strapped.
kirk doctor (not verified)
on Feb 6, 2013
the metal flexible conduit is tied in IMC with cable tie and cross under.
on Apr 24, 2013
One thing I have noted that no one else has seemed to notice is that the MC is not supported within 12 inches of the box.
Post new comment
Sign In or register to use your Electrical Construction & Maintenance (EC&M) Magazine ID
(optional)
White Papers
EC&M Learning Center
Webinars
EC&M TV
Jan. 7, 2011
video
Electrical Construction and Maintenance
Arlington non-metallic 8161 Series Boxes
Arlington’s non-metallic 8161 Series Boxes offer installation options for cameras and more, indoor or outdoor, for wet or dry locations...More
Newsletter Signup
Connect With Us