What’s Wrong Here? Hint: Shave and a Trim
Discuss this Article 16
Anonymous (not verified)
on Feb 21, 2013
it also looks like there are white wires with black tape on them. Maybe acceptable i previous edition of the code but not today.
on Feb 21, 2013
Unlikely to be able to get larger lugs for this breaker, so what other solutions are there? There looks to be space for more breakers for the doubled up terminations.
on Feb 21, 2013
Solution to the oversized wire problem would be to splice an #8 AWG to it with an approved CU/AL connector. Oversized conductor is most likely for voltage drop reduction - a few inches of #8 won't be a problem.
on Feb 21, 2013
Multiple violations, Twisted pair with one of them being white, Close shave on the bottom conductor, open bus bar(?) picture should be back a little bit further
Mike W1962
on Feb 21, 2013
I run into stuff like this alot on the job
DWBEC (not verified)
on Feb 21, 2013
1.) There's too much exposed bare copper at the breaker lugs...POOR WORKMANSHIP..AND a SHOCK HAZARD! 2.) (3) of these S.P. breaker are "Double-Lugged"!,& 3.) it appears that one "Double-Lugged" breaker has WHITE conductors connected to it
Ed S (not verified)
on Feb 21, 2013
Wires on the three pole breaker have strands cut from them to fit into the breaker. To large of wire for the breaker.
on Feb 21, 2013
Have they connected aluminium and copper conductor in same terminal?.
cjbsparky (not verified)
on Feb 22, 2013
Don't you just love it when the cut the cores to make it fit
Troy sabine (not verified)
on Feb 22, 2013
Yes looks a mess before you even start
on Feb 22, 2013
white and black are not on a 2 pole breaker..
on Feb 22, 2013
Is that parallel runs of #12???
JGE (not verified)
on Feb 22, 2013
Top c/b looks ok,Next 2 pole c/b is a violation wires are to small to be paralled 1/0 min. size. Next 3 pole c/b no phase labels or color code on wires. To much bare wire exposed at terminals. Top 2 cables have strands cut to short. Phase C cable does not match others has smaller but more strands
MikeM1951 (not verified)
on Feb 22, 2013
you can re-identify a white wire with tape if it is part of a cable assembly
on Feb 23, 2013
what an eye opener. i only saw large wire, issue totally missed smaller errors. thanks fellow electricians.beware of compliance.
mike fisher (not verified)
on Feb 25, 2013
the middle wires are double wire in a lug that is not approved for the application. The bottom wires are way oversized for the lug, trimming is not an option, and the c phase has even more trimmed.