What’s Wrong Here? Hint: Orange Crush
What is in this article?:
This photo shows where someone thought it would be okay to attach orange communication raceway (orange ENT) to a group of previously existing raceways with cable ties — in a school cafeteria, no less!
According to 800.24, communications circuits and equipment need to be "installed in a neat and workmanlike manner." Based on the uneven look of this ENT, that's definitely debatable here. This section of the Code also requires the installation to conform to 300.4(D) and 300.11.
Section 300.11(A)requires raceways to be "securely fastened in place." The ENT may be secure, but according to 300.11(B), "raceways shall be used only as a means of support for other raceways, cables, or nonelectrical equipment where the raceway or means of support is identified for the purpose, or where the raceway contains power supply conductors for electrically controlled equipment and is used to support Class 2 circuits that are solely for the purpose of connection to the equipment control circuits, or where the raceway is used to support boxes or luminaires." The existing EMT is not designed to support other raceways.
> Try Another Quiz
Discuss this Article 13
perrynillup (not verified)
on Oct 18, 2012
The orange tubing may be a PVC product which is not allowed in other than mechanical pipe systems in a room.
Frank Woznica (not verified)
on Oct 18, 2012
You cannot run gas lines in an open area in a school, where it is exposed to children...
Monk Burns (not verified)
on Oct 19, 2012
You cannot use ENT where subject to physical damage.
jim shampoe (not verified)
on Oct 19, 2012
What ever that piping is gas,water refrigeration it cannot tie up the existing electrical conduit on the wall also it is improperly hung.
MikeHoltGenius (not verified)
on Oct 19, 2012
I would be more concerned about the code violation of mechanical piping installed over the top of the disconnect on the back wall !!!!!!!!
Russ LeBlanc (not verified)
on Oct 27, 2012
Good call !!!
DavidS (not verified)
on Oct 30, 2012
My eye says that the piping was resident before the disconect was installed. Shame on the electrical contractor.
Isaac Cason (not verified)
on Oct 19, 2012
It looks like it might be HDPE conduit which is prohibited for use in buildings and exposed according to 353.12 (1) & (2)
Jim Miller, Electrical Inspector (not verified)
on Oct 19, 2012
This looks like a school where orange ENT is typically used as innerduct for Fiber Optic Network cabling per 800.110. Article 362.30 also requires support every 3 feet.
Anonymous (not verified)
on Feb 13, 2013
good call, it is ent for optic fiber!
on Oct 22, 2012
possible fireproofing issue - where the ENT penetrates the wall
rotrhead (not verified)
on Oct 24, 2012
The ENT was probably installed by a data com company that has no idea what NEC is let alone what is written in it. I have seen this type of installation in a lot of places.
British Spark (not verified)
on Nov 7, 2012
Being a British Spark , and therefore not fully knowledgeable the NEC , I would say that the standard of workmanship is very poor , ie, badly installed , not enough fixings , and why did the person that installed the PVC tube tie it on to exsisting conduit ?
I would say a second year apprentice would have done better