What’s Wrong Here? Hint: Loose Screws
What is in this article?:
An electrician discovered this pipe during a troubleshooting call. The overcurrent device protecting the circuit wires in this EMT never opened during a ground fault event. Luckily, someone noticed the pipe arcing/sparking and decided to call an electrician to check it out.
Section 250.118(4) permits EMT as an equipment grounding conductor, and 250.120(A) requires all connections, joints, and fittings be made tight using suitable tools. It appears the screws on this coupling were never tightened.
Section 250.4(A)(3) requires normally non-current-carrying conductive materials enclosing electrical conductors be connected together as well as to the electrical supply source in a manner to establish an effective ground-fault current path, which is defined in 250.2 as "an intentionally constructed, low-impedance electrically conductive path designed and intended to carry ground-fault current from the point of a ground fault on a wiring system to the electrical supply source and that facilitates the operation of the overcurrent protective device." The loose screws on the EMT coupling created a high-impedance path for fault current, which resulted in severe arcing at the coupling.
Imagine if this pipe was located in an area that was not visible. If left unchecked, the heat generated by the arcing could have easily started a fire.
> Try Another Quiz
Discuss this Article 7
Anonymous (not verified)
on Oct 4, 2012
Improper Ground
on Oct 4, 2012
Looks like someone was welding a piece on a grounded welding table with receptacles and didn't hook up the ground from the welder. Not that that every happened here of course...
Dan (not verified)
on Oct 4, 2012
Installer did not tighten set screws on coupling,but, there must be some type of current flowing n the E.MT., either fault current induced current or someone decided to use the E.MT. as a neutral.
on Oct 4, 2012
Forget the loose screws, it's obvious that this conduit is being used as a current carrying conductor.
siddig (not verified)
on Oct 5, 2012
when there is screw loose heat will occur then the joint will damage
on Oct 8, 2012
Seen this before. A 240 volt cooler had a 120 defrost timer. No neutral, but a good conduit for ground
Dave Reichman (not verified)
on Oct 9, 2012
The conductivity of die cast zinc connectors is about as poor as the conductivity of the steel EMT-about 10-25% of what a copper wire has. Looks like a great arguement for always running a green ground wire inside every conduit instead of relying on the EMT. I spent 13 years maintaining a 237 unit high rise apartment building and found many, many pulled apart EMT connections in the various shafts running up through the building. Service people would step on the conduits while repairing plumbing, etc. in the risers and that would leave kitchen receptacles un grounded as well as others in the units. Maybe its time to revise this short cut wiring method that works but leaves room for problems to occur over the life of a building. A lot of these problems with EMT could be prevented by not allowing conduit to be routed across a riser as the shortest route to an end point. All EMT should be close to a wall, etc. Maybe the 1951 code allowed this and it never happens today but.............
Post new comment
(optional)
White Papers
EC&M Learning Center
Webinars
Apr. 15, 2013
video
Protection From Arc Flashes
Learn how arc flashes happen, how they are measured and how wearing the right flame resistant clothing can keep workers safe....More
Newsletter Signup
Connect With Us