What’s Wrong Here? Hint: Keep Your Feet on the Ground
Discuss this Article 9
Dave Reichman (not verified)
on Feb 7, 2013
I don't think a Romex connector is listed as a suitable grounding apparatus for a box-or anything else for that matter.
DMT (not verified)
on Feb 19, 2013
The answer given by the ones asking the question was the proper grounding or bonding of the coaxial ground or shield. Where do they show coaxial cable? If this is the shield of a coaxial cable it is certainly larger than any coaxial I have come across.
John M (not verified)
on Feb 7, 2013
Also have dissimilar metals
mike fisher (not verified)
on Feb 9, 2013
the ground lug is to be connected to the metal box or an approved connector which a romex connector is not.
mrsafetyman110 (not verified)
on Feb 15, 2013
NEC 250.50 Electrodes include a metal underground water pipe in direct contact with earth for 10 feet or more, a metal frame of a building or structure, a concrete encased electrode, ground rod, or a ground ring.
NEC 110.14 Conductors of dissimilar metals shall not be intermixed unless the device is identified for the purpose. Listed
anti-oxidant compound shall be used on all aluminum conductor terminations, unless the device manufacturer states that it is not required.
NEC 110.14(A) In boxes with more than one grounding wire,
the grounding wires shall be tied together with a “pigtail” attached to the grounding terminal of the device.
NEC 250.64(C) The grounding electrode conductor shall be continuous, securely fastened and protected from physical
damage.
I also wonder if the pictures intended purpose was a equipotential ground? if so it should be directly to the box housing with proper approved bonding device.
on Feb 15, 2013
After looking at the answer, the entire picture is not shown in the What's Wrong Here? picture. It leaves out the box/cable box, above. Can they try to include the entire picture next time please? Thanks.
on Feb 15, 2013
Also, what about the NM cable running trough the wall hole? Is this not a violation?
Anonymous (not verified)
on Feb 17, 2013
can you connect a gfi two two cables only, no ground on this old house. only an old black and white cable
Dave Radford (not verified)
on Feb 22, 2013
Sure you can just bond the neutral to the ground lug on the device.