What’s Wrong Here? Hint: Get Back to Class
What is in this article?:
These fuses (Photo 1 above) were found during an infrared thermal scan inspection of the electrical equipment in a building. A closer look at the fuse holders reveals that Class R (rejection) type fuses should have been used in this installation. These Class H fuses do not have the notch in the blade of the fuse, which would allow it to fit around the post that is built into the fuse holder slot. The notch would allow the fuses to seat completely into the fuse holder. In fact, the cover was clearly labeled "Install Class R Fuses Only" (Photo 2 below), but the installer chose to ignore the instructions.
Section 110.9 of the 2011 NEC requires equipment intended to interrupt current at fault levels to have an interrupting rating not less than the nominal circuit voltage and the current that is available at the line terminals of the equipment. This could have been a serious problem if a fault occurred. The interrupting rating of a Class H fuse is suitable for a maximum of 10,000A of fault current. On the other hand, a Class R fuse may be capable of safely interrupting 200,000A.  That is a difference of 190,000A of energy! The Class H fuses could have exploded and caused serious equipment damage or possibly injured a person.
Photo 3 (above) shows the corrected installation, with appropriate Class R type fuses installed.
> Try Another Quiz
Discuss this Article 20
Michael (not verified)
on Jul 19, 2012
mismatched fuses
Paul Ternstrom (not verified)
on Jul 19, 2012
In addition to the fuse issue, the wiring from the switch does not appear to be 200A wiring (3/0 THHN)
Francisco Cruz (not verified)
on Jul 19, 2012
" High Leg " conductor in a 240 volts three phase fuse disconnect shall be located at right terminal .
Anonymous (not verified)
on Jul 19, 2012
That's incorrect. That's only in service rated meter sockets. Everywhere else; in panels, on breakers, in disconnect switches, they "high" leg is in the center position.
Old Spark (not verified)
on Jul 20, 2012
High leg is also supposed to be phase taped orange not red.
Richard Craver (not verified)
on Jul 19, 2012
The supply fuse clips are two small, i.e. the fuse tabs should fit inside the clips completely (securely).
David Parent (not verified)
on Jul 19, 2012
The fuses are the wrong type. They need to be type 'R' to accommodate the rejection pins in fuse clips designed for the class to which the fuse belongs.They are also lacking the proper markings.
on Jul 19, 2012
Looks like non rejection type fuse in rejection
type clip. Short circuit protection may be compromised
on Jul 19, 2012
Rejection type fuse holders with wrong class fuses installed. Likely called for current limiting fuses.
on Jul 19, 2012
fuse rejection feature in holder is defeated.
Chazz (not verified)
on Jul 19, 2012
Fusible disconnect is designed with Class R rejection clips. Fuses installed are not Class R fuses.
on Jul 19, 2012
A moron not an electrician put the fuses in That's whats wrong!!
on Jul 19, 2012
The phase conductors are brought through separate knockouts.
on Jul 20, 2012
The Handy man did it. now start arresting non licensed side jobers
on Jul 20, 2012
Wild phase is required to be in the "middle" for fuse and switch gear. Only on right hand side in a meter socket - (Three Phase Self Contained 200/320A)
on Jul 20, 2012
If this is delta with a high leg, the phase tape should be orange not red. This was a code change 20 years ago. Lots of things wrong here.
on Jul 21, 2012
not being able to see all three wires, phase rotation could be counter clock wise, wire markers could be blue - red - black instead of black - red - blue. but the main thing here is the wrong type of fuse.
Russ LeBlanc (not verified)
on Jul 28, 2012
Thanks for getting some great discussions going!
Dave Radford (not verified)
on Oct 25, 2012
Why do you all think this is a high leg, anyone think that it is a disconnect that they changed phasing on for motor rotation? Common people the fuses are the wrong type. Maybe wrong amperage too, the person who has done this must be a first year journeyman.
on Dec 8, 2012
Just read this, but congratulations, best answer
Post new comment
(optional)
White Papers
EC&M Learning Center
Webinars
Apr. 15, 2013
video
Protection From Arc Flashes
Learn how arc flashes happen, how they are measured and how wearing the right flame resistant clothing can keep workers safe....More
Newsletter Signup
Connect With Us