Ecmweb 2820 603ecmicpic1
Illustrated Catastrophes
March 1, 2006
As usual, never consider the following commentary associated with these photos as a formal interpretation of the National Electrical Code (NEC). Without criticizing anyone or any product, the following scenarios present us with serious safety questions. All references are based on the 2005 NEC. A HAIRY OVERCURRENT PROTECTION SITUATION Billie Garner, an electrician at Clark College in Vancouver, Wash.,
Billie Garner, an electrician at Clark College in Vancouver, Wash., found this ridiculous arrangement while investigating an overhead light outage in an elevator. His initial system check revealed the breaker had not tripped, and there was no power present at the light fixture. Further investigation revealed there was power to the car light toggle disconnect switch. However, after he removed the switch cover, the power was gone. When he first checked the fuses, he noticed a slight spark at the base of one unit. This is where a temporary fusing had taken place, which closed the circuit. Upon further inspection, he noticed that someone had installed a hair-like strand of wire between two terminals on the failed fuse (see fuse on left).
Whoever bypassed the overcurrent protection device created a violation of 620.61, which states that overcurrent protection shall be provided in accordance with 620.61(A) through 620.61(D). More specifically, 620.61(A) states, “Operating devices and control and signaling circuits shall be protected against overcurrent in accordance with the requirements of 725.23 and 725.24. Class 2 power-limited circuits shall be protected against overcurrent in accordance with the requirements of Chapter 9, Notes to Tables 11(A) and 11(B).”
HOMEMADE FUSES CREATE RECIPE FOR DISASTER
Derek Thomas, an eight-year journeyman electrician, ran across this installation in a mechanical loft of a new church while working for Classic Electric and Design in Plymouth Meeting, Pa. “The disconnect was feeding heating elements in air handlers,” said Thomas.
How did they get there? “Over a long Thanksgiving weekend the temperature dropped, and one of the subcontractors was screaming for heat. The HVAC contractor came in when we were not there and improvised to get the units running,” said Thomas.
The person who installed these so-called “thinwall fuses” obviously had no regard for human life or property. An overcurrent condition on this system would most likely lead to a horrible ending.
Article 240, Part VI outlines the requirements for a safe installation of cartridge fuses and fuseholders. General marking rules for fuses can be found in 240.60(C).
Found a Code Violation? E-mail your photos to Joe Tedesco at [email protected].
Joe Tedesco
