Arc flash reduction methods must be considered before working on energized electrical equipment for personnel safety. The idea behind energy reduction is to place energized electrical equipment in a state where less arc energy is available when an arcing fault occurs. These techniques range from the obvious (de-energize!) to more complex and costly engineering solutions.

Section 240.87 of the 2011 NEC, initially titled “Noninstantaneous Trip,” was added to address breakers without an instantaneous tripping function to trip breakers with no intentional delay. In the 2014 NEC, the title changed to “Arc Energy Reduction” with the intent to improve worker safety by reducing the arc flash incident energy (AFIE) on a circuit breaker that can be adjusted at 1,200A or higher.

Section 240.87 of the 2020 NEC lists seven methods to reduce arc flash energy — whether in initial design/construction or on a retrofit project. Each of the seven methods comes with pros and cons. Let’s take a look.

Method 1 – zone selective interlocking (ZSI)

ZSI establishes a higher level of sophistication by reducing intentional short-time and ground-fault delays to shorten the fault-clearing time using communications between upstream and downstream breakers. In an existing selectively coordinated system, this communication scheme permits faults to be isolated and cleared by the nearest upstream device without an intentional time delay.

Pro: Allows selective coordination for faults outside of the zone and quick response for faults inside the zone (no intentional time delay).

Con: Requires hard wiring between each device, which can get complicated and tedious to install and test, making cost a factor.

Method 2 – differential relaying

This method requires the use of programmable relays to detect and compare multiple currents to clear faults. The basic protection concept is that the current flowing into the protective zone equals the current flowing out of the protection zone. Traditionally, differential relaying is used for medium-voltage applications. This method is typically designed and installed as a custom product.

Pro: Site and application-specific.

Con: Requires installation of relays and large current transformers (CTs) with increased space requirements, adding cost.

Method 3 – energy-reducing maintenance switch (ERMS) with local status indicator

Manufacturers offer this option as an integral feature of circuit breakers that provide for installing a remote switch and indicator light. An ERMS switch is the second set of protection settings on a trip unit, typically with a lower instantaneous setting, designed to trip a breaker without any intentional delay during an arcing fault event. For example, let’s say protection settings A are used in normal operations and selectively coordinated with upstream and downstream equipment. Along with this coordinated system, there is a high AFIE. The maintenance switch is activated when performing maintenance on downstream equipment, switching to protection settings B, which alters settings to lower the AFIE. Once maintenance has been completed, the ERMS will be switched back to normal mode with protection settings A now activated (along with the higher AFIE).

This is a simple design in theory with one possible drawback: In some instances, the maintenance switch does not get switched back, leaving protection settings B still activated. This allows settings overlap or mis-coordination between that device and downstream equipment, hence the reason for the local status indicator light. This oversight can have negative consequences depending on the load it is serving and could result in nuisance tripping.

Note: Manufacturers differ in their philosophy regarding protection settings B. For example, some manufacturers’ protection settings B automatically set the instantaneous settings too low, while others allow B settings to be programmed, offering more flexibility for the engineer performing the study. He or she must understand these differing philosophies and owner requirements.

Pro: A mid-range priced solution. The indicator light for ERMS activation makes this option relatively easy to use.

Con: Human error. The switch can be left in the maintenance mode position, allowing for mis-coordination and nuisance tripping. Some manufacturers do not have flexibility in programming.

Method 4 – energy-reducing active arc-flash mitigation system

This is one of several special systems that automatically limit the energy released during an arc-fault event by one or more detection means (see Figure). The following lesser-known concepts are based on NFPA 70E, Standard for Electrical Safety in the Workplace, Annex O:

  • One concept reduces the arc duration by creating a low-impedance current path for the arcing fault, allowing the upstream breaker time to clear the fault. Essentially, this method forces a bolted fault on the circuit, which transfers electrical energy to a new path, causing the upstream breaker to operate with no intentional delay.
  • Another concept is to use an arc-flash relay with two components: light sensors to detect the light produced by the arc-flash event and a current sensor (typically a CT) to detect the sudden rise in overcurrent. These two components, when detected simultaneously, send a trip signal to the protective device to operate without intentional delay.
  • Another solution is an energy-reducing line-side isolation barrier enclosing the line-side conductors. This option protects workers from both shock and arc-flash events on the line side of the protection device.
  • Arc-resistant equipment can also be used to divert arc energy away from personnel.

Pro: Design can be specific to the end-user or specific application.

Con: Can get pricey from concept to design, installation, and testing.

Method 5 – instantaneous trip setting with temporary adjustment not permitted

When this method was originally added, the industry treated it like a temporary maintenance switch, meaning the instantaneous setting would be lowered to reduce the AFIE to an acceptable level during maintenance work. However, problems arose as workers made random adjustments to the protective settings without an engineer performing a study, calculating the actual arcing fault, and advising which settings adjustments to make.

This resulted in settings that did not lower the AFIE and falsely left workers thinking they were protected. Also, since there was no indicator light (as in Method 3), settings were often not adjusted back, or a random setting was reapplied because the worker didn’t remember the original settings. These human errors left the electrical system uncoordinated and could make the existing arc-flash label inaccurate, leading to additional unsafe work conditions. As a safeguard, a clarification added in 2020 NEC states: Temporary adjustment of the instantaneous trip setting to achieve arc energy reduction shall not be permitted.

The actual intent of this method is to have a studies engineer calculate the arcing-fault current and permanently set the protective settings to trip on this arcing current. The obvious problem with this method is that the settings might be so low that the coordination downstream is an issue and possible nuisance tripping occurs.

Pro: Inexpensive solution, which can be achieved with existing protection settings.

Con: Possible downstream coordination issues and nuisance tripping.

Method 6 – instantaneous override

An instantaneous override is a fixed, built-in factory trip setting protecting against fault currents above a breaker’s withstand capability. This setting is usually set higher than the standard instantaneous setting, and it usually protects against faults — but not always. This method should be used only when designing and installing new breakers and where the owner can have a voice in the design process. If the override function trips the breaker, coordination issues and nuisance tripping might occur.

Pro: Inexpensive option, as there are no additional costs for new equipment.

Con: Possible coordination issues; might not be an option on existing equipment.

Method 7 – approved equivalent means 

This method was included to allow for any future technology. As technology continues to evolve, any equivalent method to the six listed above can be evaluated and approved by the Authority Having Jurisdiction (AHJ). This approval is usually obtained through prior discussion between the studies engineer and the AHJ.

 Which is the best method? The methods discussed above are provided if, and only if, there is a greater danger of not de-energizing. Section 110.4(A) summarizes the intent of NFPA 70E: Energized work shall be permitted where the employer can demonstrate that de-energizing introduces additional hazards or increased risk. Of course, the best method is to de-energize the equipment.

Conclusion

What could be more dangerous than an electrocution or arc flash incident that burns or kills a worker? If there is an arc flash event in a facility and a worker is injured, the burden is on the owner to justify why they did not de-energize, and the consequences can include hefty fines and expensive lawsuits. Therefore, the priority must shift to de-energization. Owners and site operators need to find ways to shut down and perform work safely. Like personal protective equipment, these mitigation methods should be the last line of defense, not the first.

David Rewitzer, PE, CEM, is a power systems studies engineer at Hood Patterson & Dewar. He specializes in electrical safety for medium voltage and low voltage facility power distribution systems in data centers, large campuses, healthcare institutions, and commercial/industrial facilities. Dave has 30 years of experience in the electrical power industry. A licensed Professional Engineer in 13 states, he also teaches courses in arc-flash hazard awareness, electrical safety, power quality, and energy management. He is an OSHA-Authorized General Industry Trainer and participates in the IEEE 1584–2018 Guide for Performing Arc Flash Hazard Calculations and IEEE 1584.1 Guide for the Specification of Scope and Deliverable Requirements for an Arc Flash Calculation Study in Accordance with IEEE Std 1584 working groups.

Electrical Testing Education articles are provided by the InterNational Electrical Testing Association (NETA), www.NETAworld.org. NETA was formed in 1972 to establish uniform testing procedures for electrical equipment and systems. Today the association accredits electrical testing companies; certifies electrical testing technicians; publishes the ANSI/NETA Standards for Acceptance Testing, Maintenance Testing, Commissioning, and the Certification of Electrical Test Technicians; and provides training through its annual PowerTest Conference and library of educational resources.

About the Author

David Rewitzer

David Rewitzer, PE, CEM, is a power systems studies engineer at Hood Patterson & Dewar. He specializes in electrical safety for medium voltage and low voltage facility power distribution systems in data centers, large campuses, healthcare institutions, and commercial/industrial facilities. Dave has 30 years of experience in the electrical power industry. A licensed Professional Engineer in 13 states, he also teaches courses in arc-flash hazard awareness, electrical safety, power quality, and energy management. He is an OSHA-Authorized General Industry Trainer and participates in the IEEE 1584–2018 Guide for Performing Arc-Flash Hazard Calculations and IEEE 1584.1 Guide for the Specification of Scope and Deliverable Requirements for an Arc-Flash Calculation Study in Accordance with IEEE Std 1584 working groups.

Voice your opinion!

To join the conversation, and become an exclusive member of EC&M, create an account today!

Sponsored Recommendations

8 Types of Electrical Conduit and Their Uses

Electrical conduit is a tube or raceway used to house and protect electrical wires within a building or structure. From data centers to underground subways to ports and bridges...

How to Calculate Labor Costs

Most important to accurately estimating labor costs is knowing the approximate hours required for project completion. Learn how to calculate electrical labor cost.

A Powerful Duo: Fiberglass conduit and solar applications

Learn how strong, durable fiberglass conduit excelled in an environment with dense cable and helped make a complex burial much simpler for the contractor to help this customer...

Champion Fiberglass® Conduit Protects Cabling For New York's First Offshore Wind Farm

Learn how fiberglass conduit supported a heavy cable load and a buried installation to help this project reach a successful outcome.